SMT1500 using Solarwinds snmp getting UPS is over 80% load errors but data does not back that up

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1500 using Solarwinds snmp getting UPS is over 80% load errors but data does not back that up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

0 Likes
5
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

SMT1500 using Solarwinds snmp getting UPS is over 80% load errors but data does not back that up

We have a dozen or so SMT1500 that report in Solarwinds SNMP, and have issues with only one UPS. SMT1500 with NMC updated to newest firmware, UPS firmware 08.8. 

About every week or so, for an hour or two we get "UPS is over 80% load at (date, time)", one minute later it clears with a message it is back under. I have changed the logs in the UPS to record power data every one minute. We are consistantly running 7.5-8.5% W out. 

I worked with APC to update the NIC software, a few days later still doing it. The unit manufacture lists as 2014, but we just installed this unit less than a year ago, all self tests pass.

Anyone else encounter this? It is odd the rest of the same model UPS do not do this.

Labels
  • Labels:
  • Other Environmental Monitoring Products & Questions
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

About mid - July the UPS has reported the same error again so it is not resolved however is much less frequent, again checking recorded 15 second intervals of power and load show no variation. I will continue to document in case other users are experiencing the same.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

Hi Lance,

Are you sure that this is not caused by the load attached to the UPS?

If you have several SMT1500s would you be able to swap this unit with a different one and see if the problem follows the UPS or stay with the load.

-Gavan

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

Gavan, yes I have had staff in the TR when it spikes, and there is no load change. We also use Solarwinds monitoring with SNMP. Actually the reporting I am getting is from solarwinds so I was assuming this was more of a SNMP issue. We record power statistics every 15 seconds which is as small as we can get. There is never any variation in input power, output power, load, current, etc. We have other UPS with the same model and firmware not sending errors. It is odd after updating the firmware for the NIC card it reported two errors, and has not since, about 3 months, whereas it did it every three weeks or less before. Self tests pass with flying colors, and the small load never really changes more than 10%, and we are running less than 20% loaded. I will keep updating this issue for future documentation with other customers.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

The UPS keeps ringing with a bright red LED (for UPS with an LED display panel) or an LCD with an error code along with the error code. The UPS is not plugged in, the UPS is plugged in, the UPS is turned on and then off ... It is a signal that tells us that the UPS is having a motherboard fault.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

On 7/29/2020 4:53 AM, fixaf26076 said:

The UPS keeps ringing with a bright red LED (for UPS with an LED display panel) or an LCD with an error code along with the error code. The UPS is not plugged in, the UPS is plugged in, the UPS is turned on and then off ... It is a signal that tells us that the UPS is having a motherboard fault.

Your post does not appear to have anything to do with the original thread. If you are experiencing an issue with a APC UPS please start a new thread providing exact UPS model number and a detailed description of the issue. Once we have that information members of the forum may be able to assist you.

Thank you

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

0 Likes
0
1079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:30 PM . Last Modified: ‎2024-03-19 04:26 AM

About mid - July the UPS has reported the same error again so it is not resolved however is much less frequent, again checking recorded 15 second intervals of power and load show no variation. I will continue to document in case other users are experiencing the same.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of