SMT1500 Pro issue - event without alarm or total failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1500 Pro issue - event without alarm or total failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
7
1603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

SMT1500 Pro issue - event without alarm or total failure

Hello,

I have a few of the SMT1500 Pro UPS's. One of them had an issue last week. I have three pieces of equipment plugged into one UPS. Even if all three were running, the load is below the max for the UPS. Only one of the pieces of equipment was running (a thermalcycler). The thermalcycler shut off abruptly and turned back on immediately but the memory was wiped. The other equipment plugged into the UPS stayed on without issue. The UPS shows that an event occurred, but did not beep at all. Could this be a bad outlet in the back of the UPS, or some other UPS issue? If not, what kinds of events would not trigger the alarm?

Thank you,

Beth

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 1500
  • alarm
  • brown-out
  • power
  • smart
  • smart-ups
  • smt
  • thermalcycer
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

Beth,

I would suggest moving the Thermacycler to a Smart UPS and noting any difference in operation to see if the issue follows the cycler or is specific to the UPS.  Again, I think that since only this one piece of equipment had an issue on a Back UPS unit, I think the unit may require a more advanced UPS.  Do you have a Smart UPS Online unit such as the SURT series?

Regards,

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

Hi Beth,

What is the event the UPS alerted you of? Do you have this one piece of equipment plugged into a different outlet group than your other two piece of equipment?  The SMT1500 does have a single outlet group that may be configurable to such down which could very well be the case.  I would suggest verifying this and consulting the product manual if this is the case.

The manual can be found on the product page under the documentation tab below:

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=smt1500&tab=features

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

Hi Jordan,

The panel just said "event 15". I couldn't find anything in the manual about what that would mean except possibly a count of total events that had ever taken place. I just checked where all the equipment is plugged in and they are all next to each other on the back-up power side of the UPS (not the surge-only side).

Thank you,

Beth

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:18 PM . Last Modified: ‎2024-03-19 12:12 AM

Beth,

There is no surge only side on these units, they are all battery back up outlets, but thank you for confirming they are all in the same outlet group.  Does the event before event 15 list an issue?  Have you seen this issue before with this specific piece of equipment.  I am not familiar with the technology of this piece of equipment you have plugged into the UPS, but does it maybe require a pure sine wave?  It is possible that it is too sensitive to changes in voltage and switches to battery which could cause the drop on this piece only.

I would suggest swapping the plug/outlet combination of your 3 pieces of equipment to confirm this.  I doubt it is a bad outlet as the outlet is providing power, but swapping the plug/outlet combinations will verify this.  If your other two pieces of equipment continue to work fine with only this one piece of equipment dropping out during a power event on a different outlet, it looks like that piece of equipment may have specific and more advanced power needs such as 0 transfer time and a pure sine wave UPS.  Finding out what the event that triggered this issue would be helpful here, do you have a network management card to view the advanced logs?  I am under the belief it was a battery transfer that caused this drop if only one of three pieces of equipment dropped.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

Hi Jordan,
The left-hand side of the UPS is battery back-up and the right side is surge-only. I just double checked and this is the case. All equipment is plugged into the battery back-up side. All it said was "event 15" and when I scrolled through the other screens, there didn't appear to be any specific event listed. I am not sure if the thermalcycler is a pure sine wave (it uses the Peltier effect http://en.wikipedia.org/wiki/Thermoelectric_cooling) but I have had one with the power disrupted before and it just turns off, it doesn't wipe the memory and cause it to turn back on. No other power went out in the building and the source outlet has recently been inspected by an electrician.

I can try swapping out the outlet combinations to see if it changes anything, but since it was a single occurrence, I may not know if it worked for a while. I will probably just move it to another UPS and tape off the suspect outlet.

I appreciate the help.

Thanks,

Beth

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

Beth,

It sounds like your unit is a Back UPS unit and not an SMT1500, could you confirm the model number?  If this is the case, it may be even more likely that your equipment may need a more advanced UPS system.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

I just looked at it and it is a Back UPS XS 1500 (the other unit we have is a SMART unit). Maybe I should move the thermalcycler off this unit?

thanks,

Beth

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:19 PM . Last Modified: ‎2024-03-19 12:12 AM

Beth,

I would suggest moving the Thermacycler to a Smart UPS and noting any difference in operation to see if the issue follows the cycler or is specific to the UPS.  Again, I think that since only this one piece of equipment had an issue on a Back UPS unit, I think the unit may require a more advanced UPS.  Do you have a Smart UPS Online unit such as the SURT series?

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore