When I'm unselect Green Mode in Configuration -> Power Settings (NMC) and press Apply button, checkbox still checked.
How turn off Green Mode?
UPS - SMT1000I
NMC2 - AP9630
Posted: 2022-01-07 01:58 AM
The problem was in the old version of the UPS firmware (06.5). Updated to 09.6 and it worked
Posted: 2022-01-07 01:58 AM
The problem was in the old version of the UPS firmware (06.5). Updated to 09.6 and it worked