Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SMT + AP9631 issues Universal I/O at Port communication.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT + AP9631 issues Universal I/O at Port communication.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
mgallon
Crewman mgallon
Crewman

Posted: ‎2023-02-26 08:17 PM . Last Modified: ‎2023-02-26 08:22 PM

0 Likes
1
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-26 08:17 PM . Last Modified: ‎2023-02-26 08:22 PM

SMT + AP9631 issues Universal I/O at Port communication.

So odd one that I just can't work out as the fault seems to stay with the location / UPS not the AP9631 and AP9335T sensor.

Last week we had an older SMT 1500 with AP9335T that started giving the occasional SYSLOG "Environment: Lost the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication. 0x0345" so I started with a reboot of the AP9631 and the issue continued.

 

Next step was a firmware update from sumx v6.2.1 / aos v6.2.1 / bootmon v1.0.8 to sumx v7.0.8 / aos v7.08 / bootmon v1.0.9 and the issue continued for a weekend where the sensor was mostly working but tripped out about 6 times over 48 hours.

 

So today I took over a spare AP9631 that was running 7.0.3 and it then would not pickup the original AP9335T at all or a brand new AP9335TH... I took the original AP9631 card back to my desk and tried it in another SMT with a spare AP9335T and the same AP9335TH and it found them no problem at all.

 

I used the CLI commands uio -disc and ui -st and just get U1:NA and U2:NA with the original SMT where as in a spare SMT UPS the same card shows the sensors.

 

Thinking that maybe I am going mad and there is something with the SMT firmware itself that affects the AP9631 which I did not think it did. So this afternoon I did a Outputs off firmware update to UPS 15.0 (ID18) from 9.3 I think it was. Again no UIO devices are found.

Nothing has changed in the cupboard this UPS sits in for years and I'm at a bit of a loss other then just swapping out the whole UPS which I'll do tomorrow at this rate - any insight is welcome... thanks Mark

  • Tags:
  • ap9631
  • english
  • smt
  • uio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
mgallon
Crewman mgallon
Crewman

Posted: ‎2023-02-26 08:29 PM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-26 08:29 PM

I forgot to add I also tried resetting the card to defaults and doing a couple more reboots, still no sensors found. Unless I move the AP9631 to another SMT at my desk that is... most odd.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore