New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
SMC1500-2UC Issue With Beeping
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-2305:00 AM
SMC1500-2UC Issue With Beeping
Hello we have a APC 1500VA Smart UPS SMC1500-2UC rack x 2. About a month ago it started beeping on and off all day for about a minute then stops. On the displays it has a exclamation mark and says "see manual". What could be the issue? One unit is a little older and the screen stays on all the time. The other turns off after awhile. I thought that it was the battery. I replaced it and it still beeps. I'm guessing both of them are doing it. Load wise it's not being over powered. Both have a battery icon with a "X". Top one I just replaced the battery. Anyone know what the issue is?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-1305:01 AM
It looks like it's a battery fault issue. You might want to try a braindead of the UPS. See if it clears the fault or the event code changes.
1) Turn off and unplug UPS from the wall 2) Disconnect Battery 3) You may hear an audible ""click"" from the UPS. 4) Reconnect the battery, plug the unit back in the wall, and turn the UPS back on.