SMC1000-2U Issues

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMC1000-2U Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
4
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

SMC1000-2U Issues

I am running into issues with a second-hand SMC1000-2U that I acquired recently and am not sure what to troubleshoot next. When AC power is on the unit is working fine and reporting accurate information (load wattage, percentage, etc). However, when AC power is shut off (either by pulling the plug or shutting off the breaker) the UPS beeps once and power is lost to all outlets. Pressing the buttons on the UPS causes the LCD display to activate and the estimated time remaining is shown, but there is no load statistics displayed on the UPS. What steps can i try next to troubleshoot the issue further?

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
0
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

I ordered a new battery but it took some time to come in as it was on backorder. I completed additional tests and now the UPS is powering devices when on battery. Thanks for your assistance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
0
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

Hi,

When the unit is running on AC what is the load, and battery runtime reported? What you are describing indicates a bad battery but it could be an internal fault if the load is low and the battery runtime is good.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
0
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

Load is only 96W as I haven't built my rack servers yet. I have two switches, a router, and an old PC tower plugged in for testing. Estimated run time is 72 minutes and the battery indicator is full. After shutting off the power and turning it back on the UPS only shows one bar on the battery charge now with 1 minute of time remaining. This makes me think it's the battery, should I order a replacement?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
0
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

Hi,

It sounds like bad batteries. I don't have a SMC1000-2U but I think the unit has 2 12 volt batteries in series. Each good battery should read 13.5v DC and around 27v DC as a set. If they are not reading in that range the set should be replaced. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:32 AM . Last Modified: ‎2024-03-18 04:35 AM

I ordered a new battery but it took some time to come in as it was on backorder. I completed additional tests and now the UPS is powering devices when on battery. Thanks for your assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of