SMART-UPS for Mobile Production Van . . . .

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART-UPS for Mobile Production Van . . . .
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:36 AM

0 Likes
6
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:36 AM

SMART-UPS for Mobile Production Van . . . .

Hello -

I have a client building out a mobile production van that will be powered by a generator. With all the computers, displays and RAID storage I figure at it's peak it could potentially draw 2500W and even thats highly unlikely. I've never done this in a vehicle though so rather than just spec the usual I thought I'd ask around and see if anyone has any suggestions. Can I just use a typical Smart-UPS or do I need something different? Oh, and to make things even more complex, he's going to be using this in India . . . I thought the Smart-UPS RT line for Harsh Environments would be a good bet. Anyone? Thanks in advance

Tyler

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • india
  • mobile
  • production
  • van
  • vehicle
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

Thanks! I'll go with that then. Your help and expertise has been much appreciated.

Tyler

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:36 AM

0 Likes
0
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:36 AM

Tyler,

I'd say that's the best there is for that environment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

0 Likes
0
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

Thanks for the quick reply K -

I'll find out what I can about the generator. Which UPS would you recommend for 2500W in India (230V) that would be put in a Mobile Production Unit? (or I guess you need the specs on the generator first, right?) Thanks

Tyler

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

Yeah you're still looking at the very least a 5kVA UPS, which means the generator is going to have to be at least 7500w for the UPS to run online without a problem

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

What's the voltage you're getting from the generator? The problem you're going to run into is that a 3kVA UPS is only capable of around 2200W, and that's at 120V. Therefore, if we're still speaking domestic UPS power, we're looking at a minimum 5kVA UPS (as that is the next highest UPS) which will cover the 2.5kW. The problem there is that the 5kVA UPS is 208V power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

Thanks K -

So the big question - which 5k UPS would you recommend for this (keeping in mind it's going to be in India.) I was only able to come up with the APC Smart-UPS RT 5000VA 230V RM Harsh Environment - model SURTD5000RMXLI-CC. Is there a better model you would recommend? Thanks

Tyler

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-15 01:35 AM

Thanks! I'll go with that then. Your help and expertise has been much appreciated.

Tyler

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore