SMART-UPS X-3000: Internal Hardware Fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART-UPS X-3000: Internal Hardware Fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:43 AM

0 Likes
4
3559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:43 AM

SMART-UPS X-3000: Internal Hardware Fault

I am receiving the following message:  UPS: In bypass in response to an internal hardware fault. (Code : 0x011B)  This initially started after receiving the critical alert yesterday saying, "UPS: The internal battery temperature exceeds the critical threshold." (Code : 0x012C)  This message resolved itself about 2.5 hours later sending, "Informational Events - UPS: The internal battery temperature no longer exceeds the critical threshold."  The internal hardware fault message has continued.  I have attached my event and data log files.  Previous to this, the UPS has not indicated any problems during self-tests.

Is it possible this error can be cleared and all is ok again?  Or does this mean the battery or UPS itself needs replacement?

 

Thanks in advance for any help you can offer,

Carolyn K.

Attachments
logs.zip
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
3559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

Hi Carolyn,

Given the age of the batteries, it makes sense that they would need replacement. The UPS isn't showing any other issues, so it is likely that the batteries themselves were causing the temperature problems. I would recommend replacing the batteries - I think that will resolve all of the issues. When you replace the batteries in the UPS you should also replace the batteries in your external pack at the same time. Given the behavior so far, I would recommend doing this as soon as possible. Leaving them in place could result in further heating/swelling which could result in damage to the UPS and/or loss of power to your attached equipment.

Thanks!

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
3559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

Hi Carolyn,

Given the details in the log, it appears that you have an issue with either a battery failing and overheating or possibly an issue with the temperature in the physical room. It appears that on May 28th the temperature of the UPS spiked up to 99°F. Have you checked the UPS to see if the room where it is installed is overly warm? You may also want to remove the battery from the UPS to see if it feels overly hot or is swollen/bloated.

Batteries in a Smart-UPS generally last 3-5 years, but that lifespan is dramatically affected by the temperature of the install environment. If these 99°F temperatures happen with any sense of regularity you may find the lifespan of your batteries to be much closer to the 3 year mark. If you can provide the exact model/serial number of your UPS I can find the age of the unit and whether or not it is under warranty.

thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
3559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

Hi Liam,

Based on the ambient room temperature readings, the room never went above 77 F.  Checking on the room today, it's in the lower 70's.  I pulled out the battery, and it's not overly hot or swollen/bloated.  We don't generally have temperature problems in that room, except an occasional HVAC malfunction resulting in hot temperatures for no more than 2 days, which happened 2-3 times over the last 5 years.

The model number/serial number is:

Model #:  SMX3000RMLV2U - SN#IS1118000524 (we also have 1 external battery pack)

It was installed in 11/2011, so I know it is quite old.  Does this mean the battery is definitely failing?  And given the age of the unit would it make sense to get a replacement battery or replace the entire unit?

Thanks,

Carolyn

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
3560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

Hi Carolyn,

Given the age of the batteries, it makes sense that they would need replacement. The UPS isn't showing any other issues, so it is likely that the batteries themselves were causing the temperature problems. I would recommend replacing the batteries - I think that will resolve all of the issues. When you replace the batteries in the UPS you should also replace the batteries in your external pack at the same time. Given the behavior so far, I would recommend doing this as soon as possible. Leaving them in place could result in further heating/swelling which could result in damage to the UPS and/or loss of power to your attached equipment.

Thanks!

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

0 Likes
0
3559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:08 AM . Last Modified: ‎2024-03-18 02:42 AM

Thanks for your help, Liam.  I will replace them ASAP.

Carolyn

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore