Posted: 2021-06-28 11:12 AM . Last Modified: 2024-03-15 05:46 AM
Hi, I have a question about the battery. I bought this unit and I got it yasterday but the battery is still not at 100%, I installed the software and looking at the "data log" battery is charge at 99.5 max, with a load of 22,7%. It's normal or I must run the calibration that at this moment it's blank (can't select it)? Self test seem ok. Sorry for my bad english I hope that my message it's readable.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:13 AM . Last Modified: 2024-03-15 05:46 AM
Hi,
There is no need to run a calibration. If the UPS were to switch to battery it will sustain the load. A run time calibration should only be required when old batteries are replaced and the estimated run time is found to be significantly inaccurate after the replacement.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:13 AM . Last Modified: 2024-03-15 05:46 AM
Hi,
There is no need to run a calibration. If the UPS were to switch to battery it will sustain the load. A run time calibration should only be required when old batteries are replaced and the estimated run time is found to be significantly inaccurate after the replacement.