SMART-UPS 1500 RM Network management card issues

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART-UPS 1500 RM Network management card issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

0 Likes
5
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

SMART-UPS 1500 RM Network management card issues


Hi,

Looked online but couldn't find an answer.  Our UPS has been issuing messages over the past couple of weeks that it is warmstarting, randomly, mostly when logging into it but randomly as well.  This is the main culprit of an error message:

System: TCP/IP stack failure. Module: tfSheapFree-assertion error line 551, file(.\treck\source\trsheap.c)

It then warmstarts and resets it's ip address:

22-Jun-13
11:48:35

Environment: Restored the local network management
interface-to-integrated Environmental Monitor Input T Sensor (Int Sensor
at Int Sensor Loc) communication.

22-Jun-13

11:47:44

UPS: Restored the local network management interface-to-UPS communication.

22-Jun-13

11:47:17

System: Network service started. System IP is 172......... from manually configured settings.

22-Jun-13

11:47:17

System: Warmstart.

This morning I have cold booted it and reseated the network card but the error returned straight away.  Trying to find out where to from here?

Regards

Peter

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

Thanks Angela.  Yeah I think I'm getting to that point too.  Looks like a weekend job smile

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

and it's just gone through and done it again:

22-Jun-13
12:01:06

Environment: Restored the local network management
interface-to-integrated Environmental Monitor Input T Sensor (Int Sensor
at Int Sensor Loc) communication.

22-Jun-13

12:00:15

UPS: Restored the local network management interface-to-UPS communication.

22-Jun-13

11:59:48

System: Network service started. System IP is 172........... from manually configured settings.

22-Jun-13

11:59:48

System: Warmstart.

22-Jun-13

11:59:27

System: TCP/IP stack failure. Module: tfSheapFree-assertion error line 551, file(.\treck\source\trsheap.c)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

For starters, kindly check our online knowledge base ID FA156063 through our FAQ page.  It lists down all the possible causes on why would a Network Management Card do a warmstart.  Next, kindly let us know the model number of the UPS and NMC that you are using.  Then download and attach the event logs of your NMC, if this is your first time to download the event log kindly follow the steps outlined in knowledge base ID FA156131.

Kindly note the firmware that is loaded on your NMC, it would be helpful if you can update it to the latest firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

Hi Jon,

Thanks for all that.  Have followed it through and nothing out of the ordinary points to anything in the FAQ.  It is an APC Smart-UPS 1500 with an AP9617 NMC that has v3.7.2 firmware already loaded.  These events started on the 14th of June and occur randomly at 4:03am and 4:03pm and whenever the network interface is being accessed or navigated through.  The main culprit is always the event, "System: TCP/IP stack failure. Module: tfSheapFree-assertion error line 551, file(.\treck\source\trsheap.c)".  Attached are the log files:

Attachments
data.txt.zip
config.ini.zip
event.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

If it were me, I'd keep this config.ini as a backup and if possible for the card and reset your AP9617 to defaults and then either exclude the TCP/IP settings when you do that (if you cannot reconfigure the IP) or you can include that if you're able to set the IP easily. I always like to wipe everything away completely if possible. On this card, that means reset all including TCP/IP settings.

If possible, I'd let it run at default configuration after the reset for a bit just to see if it continues to do that with no configuration loaded on it (maybe for 1-2 days) and then if it runs OK, go ahead and re-upload your config.ini. I understand if after resetting to default, you need to make minimal configuration changes such as email notifications (which you can upload just parts if your config.ini file that hold this configuration if its easier).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

0 Likes
0
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:55 AM . Last Modified: ‎2024-03-05 10:43 PM

Thanks Angela.  Yeah I think I'm getting to that point too.  Looks like a weekend job smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore