Posted: 2022-12-12 03:09 AM
Hi everyone,
my SC420I reports wrong model number and line voltage(details bellow).
I tried with apcupsd, nut and serial terminal in Linux and Powerchute Business on Windows 10. Same result everywhere.
I use FTI FT232R serial to usb converver(probed different ones as well) and a geunie APC 940-0024E cable.
Any ideas whats wrong and how could I fix it?
Here is the dump if apctest:
Simulating UPSlinkCheck ...
Wrote: Y Got: SM
Attempting to use smart_poll() ...
Sent: Y Got: SM Good -- smart_poll() works!.
Going to ask for valid commands...
Wrote: a Got: 3.?=.')-89@ABDEFGKLMNOPQRSUVWXYZabcdefgjklmnopqrsuxyz~
Protocol version is: 3
Alert characters are: ?=
Command characters are: ^A^N^Z')-89@ABDEFGKLMNOPQRSUVWXYZabcdefgjklmnopqrsuxyz~
Now running through apcupsd get_UPS capabilities().
NA indicates that the feature is Not Available
UPS Status: 48
Line quality: FF
Reason for last transfer to batteries: S
Self-Test Status: NO
Line Voltage: 117.3 - SHOULD BE 230V!!!
Line Voltage Max: 117.3
Line Voltage Min: 115.9
Output Voltage: 117.3
Batt level percent: 090.0
Batt voltage: 13.20
UPS Load: 000.0
Line freq: 49.75
Runtime left: 0000
UPS Internal temp: NA
Dip switch settings: NA
Register 1: 00
Register 2: 00
Register 3: 00
Sensitivity: H
Wakeup delay: 000
Sleep delay: 180
Low transfer voltage: 106
High transfer voltage: 127
Batt charge for return: 00
Alarm status: 0
Low battery shutdown level: 05
UPS Name:
UPS Self test interval: 336
UPS manufacture date:
UPS serial number:
Date battery replaced:
Output voltage when on batteries: 115
Nominal battery voltage: 012
Percent humidity: NA
Ambient temperature: NA
Firmware revision: 10.1.D
Number of external batteries installed: NA
Number of bad batteries installed: NA
UPS model as defined by UPS: Back-UPS Pro 280 - SHOULD BE Smart-UPS SC420I
UPS EPROM capabilities string: uD43127130133136uA43108110112114uI43253257261265lD43106103100097lA43092090088086lI43208204200196e44200155090oD13115oA13100oI13230s441HMLLq44202050710p443060180300600k4410TLNr443000060180300E443336168ON OFF
The EPROM string is 205 characters long!
Hours since last self test: 000.0
That is all for now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-13 12:48 PM
Have you solved this? I am in similar situation.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-13 12:52 PM
Nope - dug the whole internet and also tried ChatGPT 😄
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-15 03:42 AM
Oh dear!