This was originally posted on APC forums on 10/6/2015
Hi there,
If we were to deploy the PCNS 4.1 appliance alongside the 3.1 we already have. So we can configure 4.1 appliance then take the 3.1 offline would there be any issues with doing so?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:47 AM
This reply was originally posted by Bill on APC forums on 10/6/2015
Ben
No. There will not be an issue unless there is an outage during the time frame and both systems are configured. You should take 3.1 off line once 4.1 is on line.