Reset Password on NMC 9631

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Reset Password on NMC 9631
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:32 AM

0 Likes
3
1352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:32 AM

Reset Password on NMC 9631

Hi; I know there is a lot of topics about this and I also found the step by step procedure to reset the password, but I am stuck. I hope you can help me.

I have a Smart-UPS RT 5000 XL: APC RT5000  with a 9631 NMC. The person who handled the IT Infrastructure is no longer here and nobody knows the password, so I am trying to reset it following this procedure: http://www.apc.com/us/en/faqs/FA156075/

I have the propietary cable, but as I don't have a serial port on my computer I have used NISUTA USB to Serial Conveter that emulates a serial port on COM3

I connect the cable to the NMC, I also disconnected the network cable from it.

I am able to connect with the cable at 9600,8,N,1,N as described, I am able to see the prompt for user id after hitting ENTER a couple of times.

Once there This is what I did/

I pressed the reset button once. Light went out.

I waited until it flashed green&orange

pressed button again, light went out.

Here comes the issue: once I hit ENTER again on Hyperterminal I got no reply from the NMC.

I tried hitting ENTER many many times, but it does not work either, I just can not move from there as there is no further answer from the NMC to hyperterminal.

I am able to do it all over again but it is always the same, I don't receive an answer after the second press on the reset button.

What else can I do?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:31 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:31 AM

Hi German,

I'll think through it in my head as I type this through you as I've done it many times.

I set up my terminal session, usually with HyperTerminal, verify I get the username/password prompt (which I don't know the password). Then, I get my paperclip and I press the pinhole reset button once, the status LED on the right (next to the checkmark and the X) goes off. I leave the paperclip held to the top of the hole (but the button isn't depressed) and wait. 5-7 seconds later, the status LED on the right alternates green and orange rapidly and I press the button a second time. The LED goes off. Immediately, I go back to the prompt on my PC and right away press enter on the keyboard once every 3-4 seconds. The prompt usually typically returns within 10-15 seconds where then I use apc for both username and password.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:32 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:32 AM

Hi German,

That sounds strange but it sounds like you're doing everything correctly too. You could try to format the NMC - this will wipe ALL settings, including TCP/IP. Resetting the password would retain all of that.

To format: 

  • Press and hold the pinhole reset button down for about 20 seconds.

If this is being performed correctly, you should see the status LED "pulsing" green. When the process is actually complete, the status LED will change its color and "pulse" orange. This is when it is time to let go. The NMC will continue to "pulse" orange a few times and then the status LED will go off, and the NMC will reboot.

A common mistake here is that some users do not making contact with the reset button so it's recommended you hold the tool you use to press and hold the reset button is held against the top of the actual pinhole.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:31 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:31 AM

Thanks Angela.  I would like to give it another try to the password wipe method before actually resetting everything.

Do you know how long should I wait for the answer from the NMC? I waited for about 1 minute as I missread the 30 seconds warning and I thought that was all the time I had, but it looks those 30 seconds count since I receive the prompt to login again.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:31 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:42 AM . Last Modified: ‎2024-03-13 01:31 AM

Hi German,

I'll think through it in my head as I type this through you as I've done it many times.

I set up my terminal session, usually with HyperTerminal, verify I get the username/password prompt (which I don't know the password). Then, I get my paperclip and I press the pinhole reset button once, the status LED on the right (next to the checkmark and the X) goes off. I leave the paperclip held to the top of the hole (but the button isn't depressed) and wait. 5-7 seconds later, the status LED on the right alternates green and orange rapidly and I press the button a second time. The LED goes off. Immediately, I go back to the prompt on my PC and right away press enter on the keyboard once every 3-4 seconds. The prompt usually typically returns within 10-15 seconds where then I use apc for both username and password.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore