Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
Hi~~
We plan to use Galaxy 5500 to replace order ups. We have some issues about 5500. What' is "Required Output Current Protection"?
Thanks for your help.

Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
Yes, 40A for each phase on the output.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
overcurrent refers to the circuit breaker size. i don't know much about 3 phase power (i deal mainly with single phase) but it seems like the UPS output (like if you wire the output to a panel), each output needs to have a 40A breaker..?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
Thanks, Angela.
For balancing 3 phase power (each phase), does APC suggest putting 40A breaker on UPS output (each single phase)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
as I am based in NAM, I asked someone EMEA for some advice. We don't require this output breaker protection in NAM.
we have checked all the Galaxy 5500 models that that we could find on the web page, it seems that all of them have this value listed at 58A besides G55TUPSM40HS - is that the one you were looking at? the installation manual for the above model states that a 58A protection is needed (there is no mention about 40A) so maybe that is incorrect anyway.
in conclusion, no matter what the correct A value is (40A or 58A), that value should be the value of the breaker/fuse per phase on the output. according to our calculations, the value should actually be 58A, so maybe the information displayed on the web page for that model is incorrect and we'll get it updated, if so.
Hope that answers your question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
Thanks for your response.
I have checked the installation manual for G55TUPSM40HS, too. There is no mention about 40A.
It really bother me that "Required Output Current Protection" and "Output Current" are different. Actually, G55TUPSM40HS is not only one (40A v.s. 58A), e.g. G55TUPSM120HS (80A v.s. 174A), G55TUPSM80HS (63A v.s. 116A) and other models.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
I got some additional information for you today.
This is for the output individual circuit protection .These protection systems ensure discrimination on all of the output circuits connected to the unit. If the recommended downstream protection is not installed, the result may be breaks in the supply of power longer than 20 milliseconds on all the other output circuits.
For the main breaker,
Regarding Neutral output current : refer below
Hope this makes sense because I don't understand it well myself ![]()
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
40A is recommended upstream protection for 40kv ups. So, maximum value is 40A on each phase, is it?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:47 AM . Last Modified: 2024-03-19 12:33 AM
Yes, 40A for each phase on the output.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.