Request for UPS in a residential installation with 5 roller shutters

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Request for UPS in a residential installation with 5 roller shutters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
SomExp
SomExp
Cadet

Posted: β€Ž2025-05-23 05:12 AM

0 Likes
3
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-23 05:12 AM

Request for UPS in a residential installation with 5 roller shutters

In my home, I have 5 roller shutters operated by tubular motors, each with a power of approximately 160W. The typical operation cycle (raising or lowering) lasts 30-40 seconds.

Assuming that all motors operate simultaneously for a full raising or lowering, I would like to know what type of UPS I need so that, in the event of a power outage, I can perform at least one or two raising and lowering cycles until power is restored.

Additionally, I am looking for a solution that:

  1. Provides me with the ability to monitor the UPS health via an application.

  2. In the event of UPS failure, allows the motors to bypass the unit and continue operating as long as power is available.

What is your recommendation for this scenario?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: β€Ž2025-05-23 06:52 AM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-23 06:52 AM

This has to be one of the strangest questions posed in this forum. πŸ€¦β€β™‚οΈ

 

Your current stated requirements either require multiple cheap (UPS) units or extra auxiliary equipment such as a ATS / Bypass.

 

Or more expensive systems that incorporate a manual bypass. 

 

As it relates to monitoring the UPS the options are buying systems that support serial connections whether via USB, RS-232, RJ50, RJ45.

 

At a base level the local monitoring depending upon specific model would use APC Power Chute Software on a local computer via USB.

 

Newer systems with a (C) SKU indicate support for APC Smart Connect (Subscription based) cloud monitoring.

 

More expensive systems also incorporate a Smart Slot for a NMC (Network Management Card) to allow complete local & remote control, monitoring, and management.

 

Your budget will dictate what path and options are available to you. I’m not sure why anyone would invest any finances and run endless power cables to a window shutter?!? 🀣

 

It would make a lot more sense to invest in a whole house generator with a ATS. Going this route would allow you to power critical systems and circuits like fridge, freezers, sump, furnace, lights, and emergency outlets.

 

Questions Ask . . . πŸ‘ 

Reply

Link copied. Please paste this link to share this article on your social media post.

bimmerdriver
Lieutenant JG bimmerdriver
Lieutenant JG

Posted: β€Ž2025-05-27 08:03 PM

0 Likes
1
600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-27 08:03 PM

If there are dedicated circuits in the breaker panel for the shutters, it would be relatively easy for an electrician to wire in a sub-panel which a UPS could be connected to. This is a strange application, so you should consider the electrical code. If not, it will be a lot more work. You will need to find out what the power factor of the motors is. Then select a UPS with a high enough VA rating based on the power factor. A 1500W UPS should be sufficient, but your licensed electrician will have to confirm that. Which UPS you use is based more on the VA rating than the Wh rating since you only require a few cycles. If you need to monitor the UPS remotely, then you either need to select a UPS that supports cloud monitoring or you need an NMC and a PC running PCNS. Of course, the PC also needs to be on the UPS, not to mention the internet connection, which will go away when the power is out.

 

A generator is probably more versatile and less of a hassle, but generators aren't inexpensive, especially considering you need to wire in a transfer switch.

Reply

Link copied. Please paste this link to share this article on your social media post.

SomExp
SomExp
Cadet

Posted: β€Ž2025-06-06 01:24 AM

In response to bimmerdriver
0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-06-06 01:24 AM

Thank you very much for your response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore