APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-29 04:50 AM . Last Modified: 2024-03-13 01:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:50 AM . Last Modified: 2024-03-13 01:20 AM
Is there a "like for like" replacement for the matrix 5000. We have three of them, and need three replacements but we can allow for runtime value to drop by 50%
Would the new UPS use the same "power out"connector as the matrix 5000 "power out"?
In these times please think cheap!
:-)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:50 AM . Last Modified: 2024-03-13 01:19 AM
it should give you your % W (wattage) and % VA (volt-amps) if supported. i think those headings would be present in the data log and maybe on the status screen.
do you see either of those values? My concern is if the 50% is wattage or VA because the matrix is 5000VA but can only supply 3750 watts as seen @ http://www.apc.com/resource/include/techspec_index.cfm?base_sku=MX5000
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:50 AM . Last Modified: 2024-03-13 01:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:50 AM . Last Modified: 2024-03-13 01:20 AM
Allow me demonstrate my ignorance by saying
"uk 240v" 🙂
Nothing particular special about the setup, so I am not sure if "step down" is needed.
I think we have come to the decision to replace it with
APC Smart-UPS RT 8000VA 230V (thanks for your advice)
One thing, if one of the old matrix 5000 were running at 50% power capacity does that mean that the load is 2500VA? How can I tell what the load is, I have a network card and can web into it, but it was not clear.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:50 AM . Last Modified: 2024-03-13 01:20 AM
the most direct replacement we'd have today would be the [Smart UPS RT line|http://www.apc.com/products/family/index.cfm?id=163]. problem is with those there is no isolation transformer like the matrix has so for 120v, you can add on an isolation transformer or a stepdown transformer for 120v.
which output voltages do you require?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:50 AM . Last Modified: 2024-03-13 01:19 AM
it should give you your % W (wattage) and % VA (volt-amps) if supported. i think those headings would be present in the data log and maybe on the status screen.
do you see either of those values? My concern is if the 50% is wattage or VA because the matrix is 5000VA but can only supply 3750 watts as seen @ http://www.apc.com/resource/include/techspec_index.cfm?base_sku=MX5000