Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Repair torn control panel ribbon cable
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-2810:28 PM. Last Modified: 2024-02-1402:35 AM
Repair torn control panel ribbon cable
I used the following steps to repair a ribbon cable that had been ripped from the control panel circuit board;
1. Cut the torn end of the cable square. Be careful not to remove so much that the cable will not reach the socket
2. Remove all excess cable at the circuit board
3. Remove a small amount of the yellow jacket
4. Carefully remove all white plastic surrounding the flat copper wires. I used a small Olfa exacto knife, being careful to not cut the flat wire.
5. Tape the ribbon cable flat against the crimped connectors on the circuit board. Ensure the red coded wire is properly aligned (don't reverse the cable!)
6. Bend the copper wires to maximize the contact with the crimped connectors
7. Solder the joints
8. Check continuity to ensure no shorts nor disconnects.
9. Note that the connection is not mechanical and therefore should not be put to undue strain.