APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:36 PM . Last Modified: 2024-03-14 04:18 AM
A customer has servers with redundant power supplies.
half by ups and half by plant protected generator
if ups goes down can powerchute sense power still being supplied on by generator?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:36 PM . Last Modified: 2024-03-14 04:18 AM
Hi,
No. PowerChute only monitors the the UPS not the generator. It will not see that AC is being provided by a generator. The solution is if the UPS is a Smart-UPS you can purchase a second Smart-UPS. Install network management cards in each Smart-UPS, install PowerChute Network Shutdown and configure that version of PowerChute to monitor both Smart-UPS. If the on on street AC goes on battery and the one being powered by the generator does not PowerChute will not react and the system will continue to run. If both Smart-UPS go on battery then PowerChute will react.
See Application Note 98 for description on running UPS in a redundant configuration.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:36 PM . Last Modified: 2024-03-14 04:18 AM
Hi,
No. PowerChute only monitors the the UPS not the generator. It will not see that AC is being provided by a generator. The solution is if the UPS is a Smart-UPS you can purchase a second Smart-UPS. Install network management cards in each Smart-UPS, install PowerChute Network Shutdown and configure that version of PowerChute to monitor both Smart-UPS. If the on on street AC goes on battery and the one being powered by the generator does not PowerChute will not react and the system will continue to run. If both Smart-UPS go on battery then PowerChute will react.
See Application Note 98 for description on running UPS in a redundant configuration.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.