Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Recalibration Question
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:18 PM. Last Modified: 2024-03-1411:15 PM
Recalibration Question
Hi all,
Two questions on recalibration.
If you have powerchute running on two UPS's (in one location with the same client on both UPS's) and you kick off a recalibration on one of the UPS's could this cause PowerChute to kick in and start a graceful shutdown?
Also in if there is only one UPS with PowerChute running and you start a recalibration when the battery is dishcharging would powerchute kick in.
In other words does powerchute understand the difference between a recalibration and a power failure?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:18 PM. Last Modified: 2024-03-1411:14 PM
Hi Phil,
Yes, PowerChute knows. When you issue a calibration via software command, the UPS should only discharge down to between 10-20% capacity and not all the way to zero.
If you're doing a calibration on older batteries (which is probably not a good idea to start), then I'd watch out for the slim, remote chance that the batteries cannot support the load at all and the UPS turns off. The bi-weekly self test should catch something like this though and if you're monitoring the UPS, you'd probably see messages warning you of other battery related problems first. Typically what happens is the UPS will cancel the calibration or refuse it in these scenarios where it knows it cannot operate on battery using its logic. If you're doing a calibration with new batteries, then there should be no concern and the UPS will not start to signal a shutdown to your equipment.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:18 PM. Last Modified: 2024-03-1411:14 PM
Hi Phil,
Yes, PowerChute knows. When you issue a calibration via software command, the UPS should only discharge down to between 10-20% capacity and not all the way to zero.
If you're doing a calibration on older batteries (which is probably not a good idea to start), then I'd watch out for the slim, remote chance that the batteries cannot support the load at all and the UPS turns off. The bi-weekly self test should catch something like this though and if you're monitoring the UPS, you'd probably see messages warning you of other battery related problems first. Typically what happens is the UPS will cancel the calibration or refuse it in these scenarios where it knows it cannot operate on battery using its logic. If you're doing a calibration with new batteries, then there should be no concern and the UPS will not start to signal a shutdown to your equipment.