Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Rackmount UPS for Generator?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Rackmount UPS for Generator?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
3
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:22 AM

Rackmount UPS for Generator?

Hello,

I've been told that I need an "online" UPS or some such to have compatibility with power coming from a generator. Specifically, it's a Honda EU2000i, which can put out 2000W. Our system load is only about 550W. We have a rack system, so I want a rack mountable UPS. What are my options? Is there something I should look for in the description that would give me compatibility?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • eu2000i
  • generator
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

Killer,

When you specified "system load", did you mean the load only powered by the UPS? Are there going to be other products/devices being powered by the generator? Typical APC sizing for the UPS to be able to run online with a generator is a minimum 3x the entire load powered by the generator. This would minimize any excessive harmonic distortion which may force the UPS on battery, and also ensure that you do not exceed 80% on the generator with the attached load(s).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:22 AM

Generally the reason why you would want an "online" UPS is because they handle "dirty" power much better than other UPS's. The reason is because they transform the power to DC and then recreate the power on the output. Obviously generators often don't produce the cleanest of power.

With regards to APC, you would be looking at a Smart-UPS RT unit. They can be found at the link below, with the smallest being a 1500.

http://www.apc.com/products/family/index.cfm?id=223

Message was edited by: EZ Button

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

Honda EU2000i is about the best you can get as far as power quality. It's output is synthesized electronically and is just as clean as the wall outlet, therefore it should work as well as the wall power.

Ordinary generators are rotational speed synched and must always spin at 1800 or 3600RPM (1500 or 3000 for 50Hz) and change in load causes both voltage and frequency swing.

Unfortunately, the lack of large external fuel tank,automatic engine start and transfer excludes the use of EU2000i as automatic backup.

If someone can start the generator and physically plug the UPS into it before its battery is exhausted, the battery runtime is as long as the availability of gasoline.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:14 AM . Last Modified: ‎2024-03-08 01:22 AM

Killer,

When you specified "system load", did you mean the load only powered by the UPS? Are there going to be other products/devices being powered by the generator? Typical APC sizing for the UPS to be able to run online with a generator is a minimum 3x the entire load powered by the generator. This would minimize any excessive harmonic distortion which may force the UPS on battery, and also ensure that you do not exceed 80% on the generator with the attached load(s).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore