Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:33 AM . Last Modified: 2024-03-11 12:59 AM
I've inherited a RT10000RMXLI which has been out of service for some time, and I've been asked to install it into a new office of the company I work for.
I can't find anyone who knows the background on the unit, so I have no idea of its status, other than it "looks" like new.
However, when I tried to test it (unloaded) by plugging it in (admittedly just on a 10-amp single-phase circuit) and pressing the on button - I get absolutely nothing - regardless of the bypass/online setting.
So, I pulled the RBC44 units out and measured them at: 84V, 78V, 42V and 42V
I know that there is a lower threshold that these APC online units require (does anyone know what it is?) but would that stop the unit from responding at all, or is this indicative of something more serious ??
Is there any way to test the unit without taking a gamble on replacing the full battery set - which is certainly not cheap.
Message was edited by: mblive
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:34 AM . Last Modified: 2024-03-11 12:59 AM
These units require good battery bus voltage for the UPS to turn on/operate in bypass. We usually say the cutoff is between 80-90v so it sounds like even though one of your batteries is close to being OK, the rest are not. Unfortunately, you would need to purchase 2 RBC44 in order to further troubleshoot.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:34 AM . Last Modified: 2024-03-11 12:59 AM
These units require good battery bus voltage for the UPS to turn on/operate in bypass. We usually say the cutoff is between 80-90v so it sounds like even though one of your batteries is close to being OK, the rest are not. Unfortunately, you would need to purchase 2 RBC44 in order to further troubleshoot.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.