Posted: 2023-04-2409:57 PM
Hello, NMC's support the generic RFC1628 MIB. If you are receiving this message, this means the logging for RFC1628 is enabled. If you do not want to see these types of events, on the NMC webUI (assuming you are using an NMC2 or NMC3), go to Configuration > Notifications > Event Actions > By Group > Select Category then RFC1628 MIB. Select the action you want to disable, if you are seeing this in the event logs, select logging, hit next until you get to the option to Enable/Disable the notification.