Important Announcement: Community Back to Full Functionality
Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.
RFC1628 MIB UPS is no longer battery
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-2409:57 PM
Hello, NMC's support the generic RFC1628 MIB. If you are receiving this message, this means the logging for RFC1628 is enabled. If you do not want to see these types of events, on the NMC webUI (assuming you are using an NMC2 or NMC3), go to Configuration > Notifications > Event Actions > By Group > Select Category then RFC1628 MIB. Select the action you want to disable, if you are seeing this in the event logs, select logging, hit next until you get to the option to Enable/Disable the notification.