Hi, anyone know if the RBC55 battery cartridges use a fuse, or simply a metal connector, to link the terminals at the non-plug end?
Z
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
Wrong. I'm looking at mine right now. Each battery pack has a blue fuse link. 32V 100A
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
I think this is a fuse type
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
hello Zane , normally they have a fuse but sometimes they have a metal connector and the fuse is in the cables of ups so you don't need another one in batteries,
regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
No fuse in the battery cable, the fuse is inside the UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:50 AM . Last Modified: 2024-03-18 03:05 AM
Wrong. I'm looking at mine right now. Each battery pack has a blue fuse link. 32V 100A