Questions on building config file for v6.2.0 firmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Questions on building config file for v6.2.0 firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
121
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:22 AM

0 Likes
5
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:22 AM

Questions on building config file for v6.2.0 firmware

Hello,

I am currently working on building our general config for the new v6.2.0 firmware. I have a few questions about the "SmartUPS/Matrix" section.

1. Does the UPSOverride portion need to be set to the UPS's serial number in order for the information in this section to be applied?

2. Can someone please explain the Low Battery Duration vs the Basic Low Battery Duration? My understanding is that the Low Battery Duration should be set to the number of remaining runtime minutes left before the "Low Battery" SNMP trap will be sent out.

     If this is correct, is there anything else that this parameter will control?

3. I am also not familiar with the PowerChute Shutdown Parameters for "Maximum Required Delay" & the Username/password (doesn't look to be the same as the login user/password). Any explanation on these would be greatly appreciated!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 1500
  • apc
  • configuation
  • matrix
  • smart_ups
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

0 Likes
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

Hi Ryan,

Here is some feedback.

1.) We sort of have this explained here for another section we use override. I'll get it updated to cover the UPS portion. http://www.schneider-electric.com/support/index?page=content&country=US〈=en&locale=en_US&id=FA156136 I'll have to confirm with the specific UPS model if you can share it but usually, the same principle explained in the article would be applied to UPS output voltage and sometimes output frequency and transfer ranges (if tied the UPS output voltage setting).

2.) Low battery duration AKA low battery signaling time is when the UPS signals it has a low battery. So you're right in your explanation. Basic Low Battery is if you're doing something special with Network Management Card (NMC) and also have a device connected to a UPS serial port and I think it is a legacy setting carried over as it does not work with some UPS models today as it used to with legacy items. Low battery state of a UPS is tied to other types of events like when the UPS starts getting close to this value and your runtime is low, you may receive messages saying batteries discharged or the batteries are too low to support the load. It is also the last point in time that the Network Management Card will send a message to PowerChute Network Shutdown clients to begin a shutdown, if they haven't already.

3.) Are you using PowerChute Network Shutdown? If so, the maximum required delay is explained a little bit here -> What does the Force Negotiation setting achieve in the Network Management Card? | FAQs | Schneider E... After the Network Management Card polls all of the PowerChute clients, it tries to determine the max amount of time any one client needs to shutdown (like to run a command file or something). The username/password pertains to the username and password tied to PowerChute Network Shutdown registration. It must be set here and also be the one you enter to install PowerChute Network Shutdown on a system. It is used as an authentication mechanism along with the authentication phrase you see on the screen. (Historically, PowerChute just required the administrator username to be the same on the Network Mgmt Card and PowerChute but now the new NMC2 firmwares support multiple users and types so we add to add a field for the user to specify it or PowerChute won't work and establish communication properly). If you're not using PowerChute Network Shutdown, then you can just leave this be.

Hope that helps. Let me know if you have any questions and can also share your UPS model. About->UPS should show you what I need within the NMC interface.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

0 Likes
0
1365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

Hi Ryan,

Here is some feedback.

1.) We sort of have this explained here for another section we use override. I'll get it updated to cover the UPS portion. http://www.schneider-electric.com/support/index?page=content&country=US〈=en&locale=en_US&id=FA156136 I'll have to confirm with the specific UPS model if you can share it but usually, the same principle explained in the article would be applied to UPS output voltage and sometimes output frequency and transfer ranges (if tied the UPS output voltage setting).

2.) Low battery duration AKA low battery signaling time is when the UPS signals it has a low battery. So you're right in your explanation. Basic Low Battery is if you're doing something special with Network Management Card (NMC) and also have a device connected to a UPS serial port and I think it is a legacy setting carried over as it does not work with some UPS models today as it used to with legacy items. Low battery state of a UPS is tied to other types of events like when the UPS starts getting close to this value and your runtime is low, you may receive messages saying batteries discharged or the batteries are too low to support the load. It is also the last point in time that the Network Management Card will send a message to PowerChute Network Shutdown clients to begin a shutdown, if they haven't already.

3.) Are you using PowerChute Network Shutdown? If so, the maximum required delay is explained a little bit here -> What does the Force Negotiation setting achieve in the Network Management Card? | FAQs | Schneider E... After the Network Management Card polls all of the PowerChute clients, it tries to determine the max amount of time any one client needs to shutdown (like to run a command file or something). The username/password pertains to the username and password tied to PowerChute Network Shutdown registration. It must be set here and also be the one you enter to install PowerChute Network Shutdown on a system. It is used as an authentication mechanism along with the authentication phrase you see on the screen. (Historically, PowerChute just required the administrator username to be the same on the Network Mgmt Card and PowerChute but now the new NMC2 firmwares support multiple users and types so we add to add a field for the user to specify it or PowerChute won't work and establish communication properly). If you're not using PowerChute Network Shutdown, then you can just leave this be.

Hope that helps. Let me know if you have any questions and can also share your UPS model. About->UPS should show you what I need within the NMC interface.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

0 Likes
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

Thanks so much! That was a lot of help!


Here is the UPS info:

Model:Smart-UPS X 1500
SKU:SMX1500RM2U
Serial Number:AS1351115090 
Firmware Revision:UPS 09.1 (ID20)

We have hundreds of UPSs that we use, so this is just one example.

One more question, what does the sensitivity change? If set to a lower value, is this just to ignore any voltage spikes or drops that quickly return to the indicated window?

We currently have ours set to normal:

UPSName=APC UPS

UPSOverride="AS1351115090"

OutputUpperVoltage=127

OutputLowerVoltage=106

Sensitivity=Normal

LowBatteryDuration=15

ShutdownDelay=90

ReturnDelay=0

SleepTime=000

BatteryDate=12/19/2013

AudibleAlarm=enabled

SimpleSignalShutdown=disabled

SimpleSignalLowBatteryDuration=120

SelfTestSchedule=OnStartUp14Since

LCDLanguage=English

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

0 Likes
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

Hi Ryan,

For SMX1500, I believe we removed the restriction on OutputUpper/Lower voltages you see there but at one time, UPS Override protected those. I am going to look into it further to see if I can get a list for different UPSs and what it protects and document it and then report back. This UPS does not have a frequency setting or output voltage setting so I don't know what else it'd protect for this specific example/UPS.

On sensitivity, we have this article here What are the different sensitivity settings of a Smart-UPS? | FAQs | Schneider Electric US. It is usually a setting that determines how sensitive a UPS is to minor power fluctuations which is something commonly adjusted when using an input power source like a generator. Typically, you'd leave this at high unless you experience frequent transfers to battery, like during a generator test.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

0 Likes
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:22 AM

Thanks a lot!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:21 AM

0 Likes
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:21 AM

Hi Ryan,

On this one, I confirmed:

On SMT/SMX/SURTD/SRT UPSes, the following are protected by UPSOverride:

- RatedOutputVoltage

- OutputFrequencyRange

On older SU, SUA, SUM, SURT, SURTA, Symmetra UPSes, the following are protected by UPSOverride:

- RatedOutputVoltage

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of