Questions for NMC and Powerchute Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Questions for NMC and Powerchute Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:13 PM

0 Likes
3
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:13 PM

Questions for NMC and Powerchute Shutdown

I haven't used Powerchute in a good number of years, so this will be essentially new to me.  We have recently gotten 3 5000 UPS and 1 3000, all with NMC 2 cards.  After some difficulty with one of the cards (it would only take a DHCP issued address, none of the other 4 methods would work), I have gotten the NMC cards on the network.  These will be on different networks, so essentially it will be one NMC for each "domain". So for example I have windows domain A, B, C and D.  These are each on a separate network which cannot talk to another. 

Unfortunately due to the way we are set up, the servers are dispersed across the network and not all the servers are actually powered by the controlling UPS.  They are powered by different UPSs (one of the 4 with NMC) across the domains.  Each UPS will be responsible for detecting a power outage and notifying servers to shutdown.  I eventually hope to put the correct servers on the correct UPSs in their respective domain, so that the affected servers are directly powered.  But I cannot do that at the moment.

Now that you have the background, my intention is to use the UPSs as shutdown providers for all the servers on the same "domain".  If I install and configure powerchute network shutdown (on each desired server) to use the NMC on it's "domain", but same network (even if it's not physically powered by the UPS) will it respond to shutdown commands?  I know I will have to do a bit of juggling to get the correct shutdown times for battery time (my problem), but I just wanted to make sure that I wasn't missing something obvious about using NMC to shutdown servers it isn't directly powering.

About rebooting.  How does that actually work?  If I keep the setting for keeping the UPS "on" when all the servers have gracefully shutdown (is this a time thing?), will the windows servers reboot automatically when the power comes back on?  How does it do this or how can I accomplish this?

What Configure event settings in PCNS and or NMC do I need to configure to accomplish my goal?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:12 PM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:12 PM

Hi,

On 6/26/2017 10:43 AM, Norman said:

Is 30 minutes the actual longest time that the UPS will remain on battery?

No, The low battery duration is how much remaining runtime is available when the UPS will signal low battery. So, if you set the low battery duration to 30 minutes when the battery reaches 29 minutes of runtime the UPS and NMC will signal low battery. All PCNS clients that are listening to the NMC will begin the OS shutdown. 

On 6/26/2017 10:43 AM, Norman said:

Is there a setting somewhere else that I can initiate shutdown if the battery drops to say, 10% capacity?

Nope. Shutdown is based on runtime. I have entered an enhancement request to allow for shutdown based on percentage. I hope to see the feature in a future release. As for now you can configure low battery on the NMC, configure PCNS to start a shutdown after the UPS has been on battery for X amount of time, or configure PCNS to start a shutdown when runtime remaining fall below X time.  Using the PCNS features you can stagger the shutdown of units. Shutdown events are discussed in the help file and User's Guide starting on page 46. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:13 PM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:13 PM

Hi,

On 6/26/2017 9:03 AM, Norman said:

If I install and configure powerchute network shutdown (on each desired server) to use the NMC on it's "domain", but same network (even if it's not physically powered by the UPS) will it respond to shutdown commands?

Yes. All systems that are on the same network segment with the NMC and configured to listen to the NMC IP address will receive a shutdown command. The NMC will send out a broadcast message that all configured PowerChute clients will react to. See Application Note 101 for more information. 

On 6/26/2017 9:03 AM, Norman said:

About rebooting.  How does that actually work?  If I keep the setting for keeping the UPS "on" when all the servers have gracefully shutdown (is this a time thing?), will the windows servers reboot automatically when the power comes back on?  How does it do this or how can I accomplish this?

In your configuration I suggest power the servers up manually since AC may be restored to the servers but not to the UPS/NMC they are listening to. If the UPS/NMC is not back on line the servers could power up and then down again. 

In most normal configurations the server is plugged into the UPS. When AC is lost the NMC informs PowerChute and the server is power down. If the NMC has been programmed to do so the UPS will cut power to it outlets and the UPS will power down. When AC is restored the UPS will power back up and restore power to the outlets. Assuming the server have been configured properly via the system BIOS the servers will power back up when AC is restored. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:13 PM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:13 PM

Thanks for the quick answers!  You have answered my pressing questions.

I do have one more question.  I was intending that my run time on battery be around 1 to 1.5 hours before shutdown.  I want to maximize the time the servers stay up. We are in a brown out area and power outages usually last no more than an hour, so i wanted to see if we could ride out the outage.  I see on the configuration menu that the low battery duration (which I read as, the amount of time on battery and off AC), is between 0-30 minutes.  Is 30 minutes the actual longest time that the UPS will remain on battery?

Is there a setting somewhere else that I can initiate shutdown if the battery drops to say, 10% capacity?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:12 PM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:14 AM . Last Modified: ‎2024-02-29 10:12 PM

Hi,

On 6/26/2017 10:43 AM, Norman said:

Is 30 minutes the actual longest time that the UPS will remain on battery?

No, The low battery duration is how much remaining runtime is available when the UPS will signal low battery. So, if you set the low battery duration to 30 minutes when the battery reaches 29 minutes of runtime the UPS and NMC will signal low battery. All PCNS clients that are listening to the NMC will begin the OS shutdown. 

On 6/26/2017 10:43 AM, Norman said:

Is there a setting somewhere else that I can initiate shutdown if the battery drops to say, 10% capacity?

Nope. Shutdown is based on runtime. I have entered an enhancement request to allow for shutdown based on percentage. I hope to see the feature in a future release. As for now you can configure low battery on the NMC, configure PCNS to start a shutdown after the UPS has been on battery for X amount of time, or configure PCNS to start a shutdown when runtime remaining fall below X time.  Using the PCNS features you can stagger the shutdown of units. Shutdown events are discussed in the help file and User's Guide starting on page 46. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of