Can someone tell me what the full load amps is on an 80kW symmetra px? i know how to do the math to determine the draw but want to know what the rated/nameplate figure is.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:50 AM . Last Modified: 2024-03-19 01:21 AM
This document will explain all the electrical specifications for input and output regarding the 80kw PX, as well as recommended breaker sizing, etc., starting on page 4 of the document.
I believe the information you are interested in is below:
Input
Input voltage - 3-phase 208V (166-240V)
Input current (nominal, per phase) - 244 A
Maximum input current (continuous, at minimum mains voltage) - 321 A
Input current protection for mains source or single mains supply (external to UPS, not supplied) - 350 A *note 3
Input current protection for bypass source in dual mains configuration (external to UPS, not supplied) - 300 A *note 4
Input frequency (progammable) - 50/60 Hz
Output
Output voltage (on line) 380 V - 3-phase 208V
Output current (nominal) - 222 A
Maximum output current (in bypass at 125% overload) - 277 A
Neutral output current (with 100% switch mode load) - 384 A *note 8
Output current protection (external to UPS, not supplied) - 300 A *note 6
Output frequency (programmable) - 50/60 Hz, Synchronized to bypass input (if present)
Notes
Recommended source connection.
1. Input electricity to be provided from a dedicated, grounded 4-wire Wye utility power source
with a grounded neutral.
2. Ensure clockwise voltage phase rotation (L1,L2,L3).
Recommended input protection (dual mains configuration).
3. Mains input: 350 Amp 3-Pole AC circuit breaker with 30 kAIC.
4. Bypass input: 300 Amp 3-pole AC circuit breaker with 30 kAIC.
Note: If your installation does not include an Isolation Transformer (optional equipment), use a
300 Amp Class “J” current limiting fuse on each input phase.
Recommended input protection (single mains configuration).
5. Mains input: 350 Amp 3-Pole AC circuit breaker with 30 kAIC.
Note: If your installation does not include an Isolation Transformer (optional equipment), use a
350 Amp Class “J” current limiting fuse on each input phase.
Recommended output (single and dual mains).
6. Output: 300 Amp 3-pole AC circuit breaker with 30 kAIC.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:50 AM . Last Modified: 2024-03-19 01:21 AM
This document will explain all the electrical specifications for input and output regarding the 80kw PX, as well as recommended breaker sizing, etc., starting on page 4 of the document.
I believe the information you are interested in is below:
Input
Input voltage - 3-phase 208V (166-240V)
Input current (nominal, per phase) - 244 A
Maximum input current (continuous, at minimum mains voltage) - 321 A
Input current protection for mains source or single mains supply (external to UPS, not supplied) - 350 A *note 3
Input current protection for bypass source in dual mains configuration (external to UPS, not supplied) - 300 A *note 4
Input frequency (progammable) - 50/60 Hz
Output
Output voltage (on line) 380 V - 3-phase 208V
Output current (nominal) - 222 A
Maximum output current (in bypass at 125% overload) - 277 A
Neutral output current (with 100% switch mode load) - 384 A *note 8
Output current protection (external to UPS, not supplied) - 300 A *note 6
Output frequency (programmable) - 50/60 Hz, Synchronized to bypass input (if present)
Notes
Recommended source connection.
1. Input electricity to be provided from a dedicated, grounded 4-wire Wye utility power source
with a grounded neutral.
2. Ensure clockwise voltage phase rotation (L1,L2,L3).
Recommended input protection (dual mains configuration).
3. Mains input: 350 Amp 3-Pole AC circuit breaker with 30 kAIC.
4. Bypass input: 300 Amp 3-pole AC circuit breaker with 30 kAIC.
Note: If your installation does not include an Isolation Transformer (optional equipment), use a
300 Amp Class “J” current limiting fuse on each input phase.
Recommended input protection (single mains configuration).
5. Mains input: 350 Amp 3-Pole AC circuit breaker with 30 kAIC.
Note: If your installation does not include an Isolation Transformer (optional equipment), use a
350 Amp Class “J” current limiting fuse on each input phase.
Recommended output (single and dual mains).
6. Output: 300 Amp 3-pole AC circuit breaker with 30 kAIC.