Proper UPS for a Server Rack with a Generator

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Proper UPS for a Server Rack with a Generator
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
tpoole
tpoole
Cadet

Posted: ‎2024-08-27 06:39 PM

0 Likes
5
1283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-27 06:39 PM

Proper UPS for a Server Rack with a Generator

Hello,

 

We have a server rack at our office and currently I have four APC Smart-UPS 1000's. I can set the voltage sensitivity on low and they work fine when we lose power and our generator is running. 

 

However, are we buying the wrong units? Should we be buying the units that have "double-conversion"?

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Kirk Teken
Kirk

Posted: ‎2024-08-28 04:26 AM

0 Likes
4
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-28 04:26 AM

Generally speaking any new hardware under consideration should be reviewed based on its specifications and the environment it’s intended to operate in. 

Once the list has been narrowed down several units should be put in place for short term evaluation & testing in the actual live environment it’s intended to be operating in.

 

If finances are not an issue double conversion systems offer the cleanest and regulated power output of all UPS topologies vs Line Interactive.

 

You’ll definitely want to validate how each system performs while on Generator power! ☝️ As you may find some model UPS do not go back (On-Line) once the generator power is fully running! 🤦‍♂️

 

Meaning, the UPS System will remain on (Battery Only) mode until such time grid power is restored. In this specific instance the batteries inside the unit will be depleted and thus initiate a shutdown of the connected loads. ☹️

 

Don’t assume the UPS only needs to run on battery mode for a short period of time because reality rarely if ever matches expectations!

 

The bottom line is to match the UPS System to the generator on site. As you’re not going to replace the building generator! 🤣

Reply

Link copied. Please paste this link to share this article on your social media post.

tpoole
tpoole
Cadet

Posted: ‎2024-08-28 06:58 AM

In response to Teken
0 Likes
3
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-28 06:58 AM

Finances are not an issue in this situation :). I want the rack to be as reliable as it can. The APC UPS' we buy, will only work if the power quality is set to low when our generator is running. So I just want to make sure we have what is best. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-08-29 03:46 AM

In response to tpoole
0 Likes
2
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-29 03:46 AM

Based on your reply that the power quality must be set to low reinforces the need to trial a demo unit on site before committing to a larger purchase.

 

The buildings power generator is obviously old and outputting dirty power. More often than not it’s due to lack of serious maintenance and calibration to insure a stable output voltage and frequency.

 

Besides the two it’s always going to be out of band THD! 

Reply

Link copied. Please paste this link to share this article on your social media post.

tpoole
tpoole
Cadet

Posted: ‎2024-08-29 06:48 AM

In response to Teken
0 Likes
1
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-29 06:48 AM

Well from my understanding the double conversion is the way to address these issues correct? 

 

The generator is 6-7 years old but we do have it serviced one per year. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-08-30 06:14 AM

In response to tpoole
0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-30 06:14 AM

A double conversion vs line Interactive topology has nothing to do with whether the hardware will operate as you expect when the building is on generator power.

 

The only difference is a double conversion system provides constant regulated pure sine wave output to the attached loads.

 

It has no baring on how the UPS will react when the AC Mains power supply is out of band / sees dirty power! ☝️

 

You can review the APC FAQ as it relates to generators: 

 

https://www.apc.com/us/en/faqs/FA158891/

 

You can also search in this APC Forum and the internet as to how many people / companies have problems with UPS while on generator power only. 

This problem is not unique to APC and affects every other UPS manufacturer on the market.

 

As you noted early on in your first post. The old system had to be adjusted to low power quality setting. This simply means the hardware was defined to accept a wider input voltage, frequency, THD.

 

In plain English, dirty power . . .  🤢

Generally speaking the vast majority of electronic hardware is designed for multi voltage / multi frequency. As such they by default are capable of accepting the perceived dirty power without issues. 👍

 

Everything else that isn’t designed with a wide operating range simply heat up or begin to operate erratically until it fails.

 

Bottom line, request a demo unit for short term trials. You’ll quickly see the results are some units require absolutely no changes in the power quality setting vs others do.

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore