Proper PCNS configuration for remote shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Proper PCNS configuration for remote shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

0 Likes
2
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

Proper PCNS configuration for remote shutdown

Hi,

Here is my current setup:
- Smart UPS SMT1000RMI2U with AP9630 NMC(connected to the switch)
- client(windows) server with PCNS installed on it(connected to thw UPS with the USB cable, connected to the switch),
- two additional Linux servers(connected to the swithc)

All 3 servers, along with the switch, are connected to the UPS.

My idea is to first gracefully shutdown two Linux servers and then client(windows) one if UPS starts working on battery.
I have already created shell script for remote shutdown of those Linux servers and it's working as expected(if I manually execute it).

Now, I've added the script into PCNS Events to perform the shutdown if condition is met but what happens is that only client(windows) machine is being powered off and not the Linux servers.
I've tried to play with Power off delays for outlet groups, set outlet where Linux machines are plugged to have shorter delay, but again only the client server gets shut down.


I think that it is pretty much clear what I want to accomplish so what would be the right way to do it, what am I missing, to which outlets should I connect my Linux machines, ...?

Best regards!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • network
  • network-management-card
  • PowerChute
  • shutdown
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

0 Likes
0
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

Hi Bill,

Thanks for your reply, it really helped me to dig a bit deeper into it.

It was all good with my scripts but the I didn't quite understand how PCNS is working. I didn't install PCNS Agents on my servers and that's why they didn't want to shutdown.

The UPS NMC communicates with each sever that has PowerChute installed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

0 Likes
0
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

Hi,

On 2/9/2017 8:16 AM, Aclys said:

- client(windows) server with PCNS installed on it(connected to thw UPS with the USB cable, connected to the switch),

1 - PCNS communicates with the UPS through the network management card not through USB. You do not need to attach the USB cable.

2 - When you run the command file manually do the Linux system shut down? If so they it may be a permissions issue. PCNS is run using a local account and it is possible the account does not have the proper credentials. We have FAQ FA159586 that discusses how to trouble shoot PCNS command file issues. 

If the command file needs to interact with the desk top you should read this post. http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/13362/-fyi-...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

0 Likes
0
825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:30 PM . Last Modified: ‎2024-03-07 12:25 AM

Hi Bill,

Thanks for your reply, it really helped me to dig a bit deeper into it.

It was all good with my scripts but the I didn't quite understand how PCNS is working. I didn't install PCNS Agents on my servers and that's why they didn't want to shutdown.

The UPS NMC communicates with each sever that has PowerChute installed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of