Problems with PCNS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problems with PCNS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
5
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

Problems with PCNS

1) I actually got PCNS 2.2.1 to install on a couple of Linux machines. Now I want to go back and change settings. I discovered how to change the username/password, IP, etc. with a bizarre string of java. But how do I change behavior for different UPS signals?

2) 2.2.1 under Windows - none of the links will do anything but display the log. How to fix (other than uninstall-reinstall)?

3) 2.2.1 under Windows - username / password no longer works. No, I did not forget it... it just stopped working. How to fix (other than uninstall-reinstall)?

4) The .bin simply will not install on many Linux and Solaris machines... gives up with a Java error about out of disk space. Obviously, "uninstall and reinstall!" won't work! So... how to move forward?

5) When is APC going to produce a version of this software that is not bloated far beyond necessary, nor require Java / X Windows? This is absolutely ridiculous... there is no reason in the world why this software could not be one or more binaries and a text configuration file available via RPM and .tar.gz This software absolutely reeks of someone trying to show off how clever they are and/or trying to justify their job.

Installing software with this functionality ought to be a short, simple task, not an exercise in mind-numbing, headache-inducing futility.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

1) I actually got PCNS 2.2.1 to install on a couple of Linux machines. Now I want to go back and change settings. I discovered how to change the username/password, IP, etc. with a bizarre string of java. But how do I change behavior for different UPS signals?

2) 2.2.1 under Windows - none of the links will do anything but display the log. How to fix (other than uninstall-reinstall)?

3) 2.2.1 under Windows - username / password no longer works. No, I did not forget it... it just stopped working. How to fix (other than uninstall-reinstall)?

4) The .bin simply will not install on many Linux and Solaris machines... gives up with a Java error about out of disk space. Obviously, "uninstall and reinstall!" won't work! So... how to move forward?

5) When is APC going to produce a version of this software that is not bloated far beyond necessary, nor require Java / X Windows? This is absolutely ridiculous... there is no reason in the world why this software could not be one or more binaries and a text configuration file available via RPM and .tar.gz This software absolutely reeks of someone trying to show off how clever they are and/or trying to justify their job.

Installing software with this functionality ought to be a short, simple task, not an exercise in mind-numbing, headache-inducing futility.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

Hey,

As for the 2rd problem, I have seen this issue a number of times. This issue is addressed in our kbase:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7098&p_created=1111676763&p...

As for the 4rd problem, the issue you mentioned usually happens when you try to install PCNS from remote server or logging using an acount other than root. If this is not the case, you can install PCNS manually. Here is what I got :

In order to install PCNS 2.2.x manually on unix/linux box , you need two files; install.jar and util.jar. The way to get these files is to use the command unzip to extract install script file. For example:

# unzip pcns221sol.bin Then you will get these two files in current work directory,save them in a temp directory like /tmp.

Once you get the 2 jar files, you need to make sure the java version on the system is 1.4.2 or higher. If java is not installed yet, you need to download it from SUN and install it on the system. You can find Java at the following link:
http://java.sun.com/javase/downloads/index.jsp

Next, You need to make sure Xwindows is installed on this computer. A remote display is not supported.

After java is properly installed and X-windows is running on the system, open a command line interface and make sure that you are in the same directory as install.jar and util.jar. Run the command as follows:
#java –cp .:install.jar:util.jar load

The installer should pop up at this point.

I hope it hepls. let me know the results.

Message was edited by: annwang

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

To fix the space problem, search the Linux machine for any type of PowerChute installed, any folder that contains information regarding PCNS, delete it. After that, reboot the machine, and you should have no problem installing PCNS.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

Sorry to invade to this thread, Can any expert advise me what is the syntax of shut down command file in a Linux server? Pls provide an example. I want to shut down the database of the server on the event of 'on battery' , with a script.

I have to put the command file on both pages of 'Configure events' and shut down configuration page?

Thanks for any reply

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

If you want the command file to run only one specific event, for example on "UPS: On Battery", you would only select the command file option under that event and leave the option under "Configure Shutdown" alone.

If you want the Command File to run in any event of shutdown, you will need to set the command file in the "Configure Shutdown" section of PCNS. This basically makes running the command file a blanket rule, as opposed to the "Configure Event" option which only makes the cmd file run for a single event occurence.

Maybe one of our Non-APC forums users can help with the Linux command file request.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

1) I actually got PCNS 2.2.1 to install on a couple of Linux machines. Now I want to go back and change settings. I discovered how to change the username/password, IP, etc. with a bizarre string of java. But how do I change behavior for different UPS signals?

2) 2.2.1 under Windows - none of the links will do anything but display the log. How to fix (other than uninstall-reinstall)?

3) 2.2.1 under Windows - username / password no longer works. No, I did not forget it... it just stopped working. How to fix (other than uninstall-reinstall)?

4) The .bin simply will not install on many Linux and Solaris machines... gives up with a Java error about out of disk space. Obviously, "uninstall and reinstall!" won't work! So... how to move forward?

5) When is APC going to produce a version of this software that is not bloated far beyond necessary, nor require Java / X Windows? This is absolutely ridiculous... there is no reason in the world why this software could not be one or more binaries and a text configuration file available via RPM and .tar.gz This software absolutely reeks of someone trying to show off how clever they are and/or trying to justify their job.

Installing software with this functionality ought to be a short, simple task, not an exercise in mind-numbing, headache-inducing futility.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of