Problems with 2 UPS units

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problems with 2 UPS units
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
SmlBizAdmin_apc
SmlBizAdmin_apc
Cadet

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:34 AM

0 Likes
3
1370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:34 AM

Problems with 2 UPS units

I have a problem with 2 different UPS units, each has a different server plugged into it.

#1. APC Smart-UPS 1500 with a server running Server 2012 R2 plugged into it and the latest version of the PowerChute Business Edition software installed (correct version for 2012 R2). This server has been connected to the UPS by both a USB and then a DB9 cable but the UPS does not show up in the APC Business Edition Device List Configuration window. The correct subnet is supplied and the IP of the management card in the UPS can be pinged and connected to via a browser where I've logged in and I believe configured it correctly. But it won't appear in the device list. It doesn't show up in Device Manager either. What needs to be done to get this UPS to show up and be managed in the PowerChute software?

#2. Server is an old Windows 2003 server getting decommissioned soon. But in the meantime I'm trying to manage it and the UPS it's plugged into. This UPS is an older one that does not have a management card in it. The UPS shows in Device Manager and when I run the PowerChute Business Edition Device List Configuration the server shows as a Discovered Device. I select it, click Add to add it to the Current Device List and click Apply. A message then appears in the window that it's preparing to add the server to the device list. But then that changes to the error that says it failed to apply the configuration profile to the server. I have no idea what is wrong and what to do to. There are no errors in the event logs of the server, I only get that error message in the APC software which doesn't provide any help.

Jonathan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

0 Likes
0
1370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

Hi,

On 3/17/2016 9:47 AM, Jonathan said:

Per #2, I don't know what you mean by the PBEAgent web interface. If you're referring to the console that is installed as part of the Business Edition installation, then yes I have no problem logging into it. If you're referring to logging into something using a web browser, then I don't know what that would be. In scenario #2 I don't use a web browser for anything.

All PowerChute Business Edition Agents have a web interface. The Agent is the piece of the application responsible for communicating to and from the UPS. You can access the interface from a browser (Firefox, IE, Chrome) by entering http://system IP address:3052 or https://system IP address:6547 The PBEServer only gathers information from the Agent/s. The PBEConsole is the GUI that displays the information gathered by the PBEServer. 

In most installations I recommend only using the web interface unless you are purchasing the Deluxe 25 node version to monitor 25 Agent from 1 central location. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:34 AM

0 Likes
0
1370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:34 AM

Hi,

On 3/15/2016 4:32 PM, Jonathan said:

#1. APC Smart-UPS 1500 with a server running Server 2012 R2 plugged into it and the latest version of the PowerChute Business Edition software installed (correct version for 2012 R2). This server has been connected to the UPS by both a USB and then a DB9 cable but the UPS does not show up in the APC Business Edition Device List Configuration window. The correct subnet is supplied and the IP of the management card in the UPS can be pinged and connected to via a browser where I've logged in and I believe configured it correctly. But it won't appear in the device list. It doesn't show up in Device Manager either. What needs to be done to get this UPS to show up and be managed in the PowerChute software?

Is the system on the same network segment and the system running PBEServer? If not open the Device List Configuration Wizard and click on Configure discovery and add the network segment. If the system is in the same network segment the issue may be caused by a miss-matched user name or password. If the user name and password used for the PBEAgent does not match the PBEServer the PBEAgent will not be discovered. 

On 3/15/2016 4:32 PM, Jonathan said:

#2. Server is an old Windows 2003 server getting decommissioned soon. But in the meantime I'm trying to manage it and the UPS it's plugged into. This UPS is an older one that does not have a management card in it. The UPS shows in Device Manager and when I run the PowerChute Business Edition Device List Configuration the server shows as a Discovered Device. I select it, click Add to add it to the Current Device List and click Apply. A message then appears in the window that it's preparing to add the server to the device list. But then that changes to the error that says it failed to apply the configuration profile to the server. I have no idea what is wrong and what to do to. There are no errors in the event logs of the server, I only get that error message in the APC software which doesn't provide any help.

You should verify that you can log into the PBEAgent web interface. If there is a communication issue between the Agent and the UPS the Agent will fail to communicate properly with the PBEServer. You should also verify the user name and password match.  

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

SmlBizAdmin_apc
SmlBizAdmin_apc
Cadet

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:34 AM

0 Likes
0
1370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:34 AM

Bill, thanks for responding.

The same user name and password is used for all APC software on both servers and I've verified it multiple times, so that I can rule out.

All servers and UPS units are on the same subnet.

Per #1 I've tried adding the subnet multiple times to scan but it never finds the SmartUPS even though I can connect to and login to its web interface with no problem. The APC software just doesn't see it.

Per #2, I don't know what you mean by the PBEAgent web interface. If you're referring to the console that is installed as part of the Business Edition installation, then yes I have no problem logging into it. If you're referring to logging into something using a web browser, then I don't know what that would be. In scenario #2 I don't use a web browser for anything.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

Hi,

On 3/17/2016 9:47 AM, Jonathan said:

Per #2, I don't know what you mean by the PBEAgent web interface. If you're referring to the console that is installed as part of the Business Edition installation, then yes I have no problem logging into it. If you're referring to logging into something using a web browser, then I don't know what that would be. In scenario #2 I don't use a web browser for anything.

All PowerChute Business Edition Agents have a web interface. The Agent is the piece of the application responsible for communicating to and from the UPS. You can access the interface from a browser (Firefox, IE, Chrome) by entering http://system IP address:3052 or https://system IP address:6547 The PBEServer only gathers information from the Agent/s. The PBEConsole is the GUI that displays the information gathered by the PBEServer. 

In most installations I recommend only using the web interface unless you are purchasing the Deluxe 25 node version to monitor 25 Agent from 1 central location. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore