Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Problem with interface expanders

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problem with interface expanders
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:47 PM . Last Modified: ‎2024-03-14 11:43 PM

0 Likes
1
560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:47 PM . Last Modified: ‎2024-03-14 11:43 PM

Problem with interface expanders

I recently bought 2 new sua1500rm2u ups's and 2 ap9607 interface expanders. The servers on the expanders serial interfaces do not see the ups and will not install the agent(old v. 6.5 I think). I have a mix of windows 2k8 and 2k3 machines. I was hoping to keep that version of the software so that I could have the server peice for managment, but is that where my problem lies?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:47 PM . Last Modified: ‎2024-03-14 11:43 PM

0 Likes
0
560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:47 PM . Last Modified: ‎2024-03-14 11:43 PM

hi

let me go over a couple of items with you.

1.) the cable that is physically connected to the smart signaling port on the UPS itself should be connected to the server using the 940-0024 or 940-1524 DB9 APC cable. when you install Powerchute business edition (which I will provide a link at the bottom of this post), you can have the UPS be autodetected during the installation or choose a Smart UPS in Smart signaling mode. once you access the interface that i note below, you should be able to make changes to the UPS configuration, see available runtime, and current voltages, etc

2.) the servers that are physically connected to the AP9607 serial expanders should be using the 940-0020B cable. when you install the powerchute business edition agent on them, you need to specify a Smart UPS in SIMPLE signaling with interface expander mode. the UPS wont be auto detected I dont think.

so to confirm, each server needs to be physically connected in the right spot with the correct cable and then with the software installed, be set to the correct communication type. when you login to a simple signaling agent, you only will see either "online" or "on battery" for the status and that is it - no voltages, runtime, etc so it could look like its not working correctly. the UPS will only tell these simple signaling agents when it has a low battery which will tell them to shutdown.

you can find powerchute business edtion 8.0.1 [at this link|http://www.apc.com/tools/download/software_comp.cfm?sw_sku=SFPCBE801&id=125&family=&part_num=&swfam=...]. keep in mind, each agent installed on each server, will be accessible via a web browser at http://:3052 or via http://127.0.0.1:3052 - if you are looking to keep track of multiple computers, you may look into powerchute business edition deluxe to be able to manage 5 or up to 25 agents from one GUI. you mentioned you have an older version of PCBE. can you confirm what exactly you have installed? powerchute business edition deluxe is comprised of three components - an agent, server, and console. you need to have all the same versions of all three components installed for everything to work correctly. APC recently changed the software though so before you remove anything, let us know what you have.

also, you could look into putting a network management card into your UPS(s) and shutting down everything over the network depending on your overall set up.

hope this helps! let us know if you have any questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:47 PM . Last Modified: ‎2024-03-14 11:43 PM

0 Likes
0
561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:47 PM . Last Modified: ‎2024-03-14 11:43 PM

hi

let me go over a couple of items with you.

1.) the cable that is physically connected to the smart signaling port on the UPS itself should be connected to the server using the 940-0024 or 940-1524 DB9 APC cable. when you install Powerchute business edition (which I will provide a link at the bottom of this post), you can have the UPS be autodetected during the installation or choose a Smart UPS in Smart signaling mode. once you access the interface that i note below, you should be able to make changes to the UPS configuration, see available runtime, and current voltages, etc

2.) the servers that are physically connected to the AP9607 serial expanders should be using the 940-0020B cable. when you install the powerchute business edition agent on them, you need to specify a Smart UPS in SIMPLE signaling with interface expander mode. the UPS wont be auto detected I dont think.

so to confirm, each server needs to be physically connected in the right spot with the correct cable and then with the software installed, be set to the correct communication type. when you login to a simple signaling agent, you only will see either "online" or "on battery" for the status and that is it - no voltages, runtime, etc so it could look like its not working correctly. the UPS will only tell these simple signaling agents when it has a low battery which will tell them to shutdown.

you can find powerchute business edtion 8.0.1 [at this link|http://www.apc.com/tools/download/software_comp.cfm?sw_sku=SFPCBE801&id=125&family=&part_num=&swfam=...]. keep in mind, each agent installed on each server, will be accessible via a web browser at http://:3052 or via http://127.0.0.1:3052 - if you are looking to keep track of multiple computers, you may look into powerchute business edition deluxe to be able to manage 5 or up to 25 agents from one GUI. you mentioned you have an older version of PCBE. can you confirm what exactly you have installed? powerchute business edition deluxe is comprised of three components - an agent, server, and console. you need to have all the same versions of all three components installed for everything to work correctly. APC recently changed the software though so before you remove anything, let us know what you have.

also, you could look into putting a network management card into your UPS(s) and shutting down everything over the network depending on your overall set up.

hope this helps! let us know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of