Problem with accessing network management cards remotely

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problem with accessing network management cards remotely
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:20 PM

0 Likes
8
2308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:20 PM

Problem with accessing network management cards remotely

We have several sites across the world where i'm having problems accessing the GUI's in Internet Explorer and Firefox from the UK.  I can however access them via telnet and when in country?

Example...

Ghana we have several UPS being monitored. AP9630s and AP9631s card installed.  All are running v6.0.6.  The local supprt guy based in Accra can access all the UPS remotely in the country via the GUI.  When i try to access from the UK I am unable to except via telnet.  A guy in Nigeria has also tried to access the UPSs in Ghana and cannot.  This isn't just limited to Ghana, it is sever sites across the EMEA region.

Our WAN and LAN teams have checked the firewalls and network bits and see no reason why i cannot access them?  Has anybody else come across this problem before?

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • access
  • ap9630
  • ap9631
  • gui
  • remote
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

0 Likes
0
2305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

Ok, I'll add you as a friend so that if the opportunity comes up, I can private message you some details. Thanks for your patience and help!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:20 PM

0 Likes
0
2307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:20 PM

Sounds like what we have documented here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA235265 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:20 PM

0 Likes
0
2306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:20 PM

Hi Angela

Thanks for the info I've tried the work around now and although it has seemed to make some difference it's not fixed the issue.  I've had to use a smalled MTU than the 1300 recommended in the workaround.

C:\>ping 10.147.154.237 -f -l 1273

Pinging 10.147.154.237 with 1273 bytes of data:
Packet needs to be fragmented but DF set.
Packet needs to be fragmented but DF set.
Packet needs to be fragmented but DF set.
Packet needs to be fragmented but DF set.

Ping statistics for 10.147.154.237:
    Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),

C:\>ping 10.147.154.237 -f -l 1272

Pinging 10.147.154.237 with 1272 bytes of data:
Reply from 10.147.154.237: bytes=1272 time=81ms TTL=250
Reply from 10.147.154.237: bytes=1272 time=81ms TTL=250
Reply from 10.147.154.237: bytes=1272 time=94ms TTL=250
Reply from 10.147.154.237: bytes=1272 time=58ms TTL=250

Ping statistics for 10.147.154.237:
    Packets: Sent = 4, Received = 4, Lost = 0 (0% loss),
Approximate round trip times in milli-seconds:
    Minimum = 58ms, Maximum = 94ms, Average = 78ms

netsh>interface ipv4 show subinterface

   MTU  MediaSenseState   Bytes In  Bytes Out  Interface
------  ---------------  ---------  ---------  -------------
  1500                1  692723679  483697084  Ethernet
4294967295                1          0     169057  Loopback Pseudo-Interface 1
  1500                2  307088215  143704572  Wi-Fi
  1272                5          0          0  Local Area Connection* 2

I then tried to access the UPS on Internet Explorer and Firefox with no luck.

There is a way to downgrade the firmware on the UPSs correct?  What was the last version of firmware that didn't hhave this issue?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

0 Likes
0
2306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

Hi Angela

I was changing the wrong interface.  Now i've changed the correct one it's working fine and i can connect to the UPSs.

Is there a time frame for this fix?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

0 Likes
0
2306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

I don't have a confirmed time frame but it is something I am constantly driving to escalation on behalf of customers as the impact to you and other customers is high (and annoying). I will add your case/issue to our bug report as yet another case and to re-iterate the priority. I know someone is actively working on it but last I checked, we did not have a fix confirmed.

I forgot, if you prefer to downgrade, firmware v5.X.X does not have this issue. If you were interested in considering downgrading, please read here first -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA167693 and I could provide the older firmware if you'd like to do that. I am not sure if you've ever used the older firmware as it is quite different and does not have as many features (SSL/TLS email authentication, multiple user login/accounts, etc) but of course has this issue you're seeing. v5.X.X has an older blue/white interface if you've ever seen it..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

0 Likes
0
2307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

I've changed the MTU on a few or our desktops and laptops and we will get by for the time being.

Thank you again for your time, effort and information! laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

0 Likes
0
2307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

No problem! We have someone dedicated dealing with it this week to wrap it up. I can't make any promises but if we have a beta that could be made available, would you be interested in testing it on one of your devices and seeing if putting your MTU back to what it was with the new firmware works as it should?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

0 Likes
0
2308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

Yes sure!  I have a site in London that we could test it on to start with.  I wouldn't want to use the Africa ones straight away as alot of those sites are very remote and hard to get to.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

0 Likes
0
2306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:18 AM . Last Modified: ‎2024-02-29 11:15 PM

Ok, I'll add you as a friend so that if the opportunity comes up, I can private message you some details. Thanks for your patience and help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore