Prevent the TURN OFF POWER of Outlet Groups in case of a 5 minutes power outage when power on comes

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Prevent the TURN OFF POWER of Outlet Groups in case of a 5 minutes power outage when power on comes
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ThomasH_apc
ThomasH_apc
Cadet

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
5
1013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Prevent the TURN OFF POWER of Outlet Groups in case of a 5 minutes power outage when power on comes

The following has happened:

During a five minutes power outage a server was shutting down (shutdowntime 120 seconds). The shutdown takes longer as expected because a windows update. The power off timer on UPS display began to countdown from 180 to 160 and the power came on again this period.

I had expected that the power off countdown will interrupted if power is on, but it wasn't.

Is my UPS SMT1000 out of order or is this behaviour by design?

If yes, how can I prevent this?

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
1012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi Thomas,

That makes sense. Are you using a network management card (NMC) and PowerChute Network Shutdown (PCNS), or are you using PowerChute Business Edition (PCBE)?

I don't have a way to abort the shutdown, but some things to think about:

Typically if the worst-case shutdown time is 15 minutes, then the system should be configured to shut down when runtime drops below 15 minutes with a power off delay of 15 minutes. That way the computer will always have enough time for a clean shutdown. To do this, in outlet settings configure the power off delay to be 15 minutes and then you have a few options:

- Configure "load shedding" in the outlet settings to start a shutdown when runtime drops below 15 minutes. Be sure to uncheck "skip outlet off delay".

- Change "low battery duration" to 15 minutes -- this causes PCNS agents attached to any outlet to start shutting down.

- Configure PCNS on the server in question to start shutting down when runtime remaining is less than 15 minutes.

If a significant amount of that 15 minutes is windows update, you might try forcing windows update not to run during an emergency shutdown. Microsoft doesn't seem to make it easy, but it seems like you might be able to make a shutdown script that deletes everything in "%windir%\softwaredistribution\"

You could also avoid having the UPS shut down at all. PCNS has an option to (or not to) send the turn off signal to the UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
1012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi,

On 3/19/2018 5:53 PM, Thomas said:

Is my UPS SMT1000 out of order or is this behaviour by design?

This is works as designed. Once the shut down process has started it must complete before restarting. 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
1012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

To add to Bill's answer, if the UPS aborted its shutdown, the server would still shut down and remain off. So the UPS needs to cycle the power so the server can turn back on.

Reply

Link copied. Please paste this link to share this article on your social media post.

ThomasH_apc
ThomasH_apc
Cadet

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
1012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

thanks all for fast reply. I understand that this behaviour is necessary.

But in my case it isn't wished, because:

One of my attached devices is a big workstation with more than 20 hyper-v VMs.

And it happens that the OS shutdown takes a lot longer as expected because the VMs and in case of a additional update on windows update during OS shutdown.

Normally it takes only 3 minutes. Worst it takes 15 minutes. But then the power is cut off from usv.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
1012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi,

Are you running PowerChute Business Edition or PowerChute Network Shutdown and which version? If Network Shutdown what is the model of the UPS Network Card and what firmware is on the card. Also, what is the model UPS. You will find the model information on the bar code sticker. 

Liz5UX33IjItXDHyijM61g%3D%3D.pngLiz5UX33IjItXDHyijM61g%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
1013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:18 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi Thomas,

That makes sense. Are you using a network management card (NMC) and PowerChute Network Shutdown (PCNS), or are you using PowerChute Business Edition (PCBE)?

I don't have a way to abort the shutdown, but some things to think about:

Typically if the worst-case shutdown time is 15 minutes, then the system should be configured to shut down when runtime drops below 15 minutes with a power off delay of 15 minutes. That way the computer will always have enough time for a clean shutdown. To do this, in outlet settings configure the power off delay to be 15 minutes and then you have a few options:

- Configure "load shedding" in the outlet settings to start a shutdown when runtime drops below 15 minutes. Be sure to uncheck "skip outlet off delay".

- Change "low battery duration" to 15 minutes -- this causes PCNS agents attached to any outlet to start shutting down.

- Configure PCNS on the server in question to start shutting down when runtime remaining is less than 15 minutes.

If a significant amount of that 15 minutes is windows update, you might try forcing windows update not to run during an emergency shutdown. Microsoft doesn't seem to make it easy, but it seems like you might be able to make a shutdown script that deletes everything in "%windir%\softwaredistribution\"

You could also avoid having the UPS shut down at all. PCNS has an option to (or not to) send the turn off signal to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of