PCNS not shutting down machine

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS not shutting down machine
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
7
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

PCNS not shutting down machine

I have AP9631 installed on a SUA 2200I, which is used to control PCNS for 3 windows server 2012 R2 machines.

NMC is already connected to all 3 machines and all of them are listed.

Thing is, a blackout just happened and it doesn't seem to work properly

03/19/2018 22:13:11 UPS is no longer running on battery power or output power has been turned on.
03/19/2018 21:09:13 UPS has switched to battery power.

I already set config shutdown > Runtime remaining below threshold to 900 secs, but as you can see, during 1 hour blackout there's no shutdown event happened.

I always have certificate error whenever i want to access the web page.. is it related somehow?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi,

"Last state" may work. "Always on" should have. PowerChute runs shutdown.exe with these parameters shutdown /s /f /t %delay% /d UP:6:12 /c "PowerChute Network Shutdown has initiated a system shutdown." %delay% = 60 seconds

As with any other software once the system has been powered down the software cannot control the systems behavior. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi,

Would you provide the PCNS EventLog, pcnsconfig.ini and the event.log form the NMC? The PCNS files will be found in C:\Program Files\APC\PowerChute\group1 assuming you installed to the default path. 

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

On 3/20/2018 1:55 AM, Bill said:

Hi,

Would you provide the PCNS EventLog, pcnsconfig.ini and the event.log form the NMC? The PCNS files will be found in C:\Program Files\APC\PowerChute\group1 assuming you installed to the default path. 

Last night I noticed the NMC timezone isnt correct yet so i syncronized it 

The related log file part should be on date 03/17/2017, but strangely none seems to mention a blackout or somehting

03/17/2018 17:00:36 UPS has switched to battery power. .3.5.1.5.4.1

03/17/2018 17:00:38 UPS is no longer running on battery power or output power has been turned on. .3.5.1.5.4.2

03/17/2018 20:50:53 PowerChute is attempting to open UDP port 3052. .3.4.9.9

03/17/2018 20:50:53 PowerChute successfully opened UDP port 3052. .3.4.9.9

03/17/2018 20:51:20 Communication has been established. .3.5.1.5.6.1

03/17/2018 20:51:20 PowerChute Network Shutdown version 4.2.0 monitoring started. .3.5.1.5.6.10

03/17/2018 20:51:21 PowerChute is attempting to open TCP port 3052. .3.4.9.9

03/17/2018 20:51:21 PowerChute is attempting to open TCP port 6547. .3.4.9.9

03/17/2018 20:51:21 PowerChute successfully opened TCP port 3052. .3.4.9.9

03/17/2018 20:51:21 PowerChute successfully opened TCP port 6547. .3.4.9.9

03/17/2018 20:51:50 Available runtime has been exceeded. .3.5.1.6.1

03/17/2018 21:18:44 PowerChute is attempting to open UDP port 3052. .3.4.9.9

03/17/2018 21:18:44 PowerChute successfully opened UDP port 3052. .3.4.9.9

03/17/2018 21:19:11 Communication has been established. .3.5.1.5.6.1

03/17/2018 21:19:12 PowerChute Network Shutdown version 4.2.0 monitoring started. .3.5.1.5.6.10

03/17/2018 21:19:13 PowerChute is attempting to open TCP port 6547. .3.4.9.9

03/17/2018 21:19:13 PowerChute is attempting to open TCP port 3052. .3.4.9.9

03/17/2018 21:19:13 PowerChute successfully opened TCP port 3052. .3.4.9.9

03/17/2018 21:19:13 PowerChute successfully opened TCP port 6547. .3.4.9.9

03/17/2018 21:19:42 Available runtime has been exceeded. .3.5.1.6.1

03/17/2018 21:36:17 PowerChute is attempting to open UDP port 3052. .3.4.9.9

03/17/2018 21:36:17 PowerChute successfully opened UDP port 3052. .3.4.9.9

03/17/2018 21:36:43 Communication has been established. .3.5.1.5.6.1

03/17/2018 21:36:44 PowerChute Network Shutdown version 4.2.0 monitoring started. .3.5.1.5.6.10

03/17/2018 21:36:45 PowerChute is attempting to open TCP port 6547. .3.4.9.9

03/17/2018 21:36:45 PowerChute is attempting to open TCP port 3052. .3.4.9.9

03/17/2018 21:36:45 PowerChute successfully opened TCP port 3052. .3.4.9.9

03/17/2018 21:36:45 PowerChute successfully opened TCP port 6547. .3.4.9.9

03/17/2018 21:37:13 Available runtime has been exceeded. .3.5.1.6.1

03/17/2018 22:42:57 PowerChute is attempting to open UDP port 3052. .3.4.9.9

03/17/2018 22:42:57 PowerChute successfully opened UDP port 3052. .3.4.9.9

03/17/2018 22:43:24 Communication has been established. .3.5.1.5.6.1

03/17/2018 22:43:24 PowerChute Network Shutdown version 4.2.0 monitoring started. .3.5.1.5.6.10

03/17/2018 22:43:24 PowerChute is attempting to open TCP port 6547. .3.4.9.9

03/17/2018 22:43:24 PowerChute is attempting to open TCP port 3052. .3.4.9.9

03/17/2018 22:43:25 PowerChute successfully opened TCP port 3052. .3.4.9.9

03/17/2018 22:43:25 PowerChute successfully opened TCP port 6547. .3.4.9.9

03/17/2018 22:43:54 Available runtime has been exceeded. .3.5.1.6.1
Attachments
group1.7z
Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Ah after a phone call with APC CS here i figured it out..

I mistook remaining threshold with battery on UPS..

Changed it already to Battery on UPS, gonna see next blackout if it works..

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Ok, it seems to work for PC that is connected using serial (havent tested for other connected PC because the blackout was too quick)

There was just one problem,

after the power is restored, my PC wont turn back on.

BIOS is set to auto turn on after power loss (cant remember the exact name)  

Without PCNS it was working,

but now after being shutdown by PCNS, it wont turn back on again.. any idea?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi,

You may need to change the BIOS setting to always on See this post http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/12332/power...

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Unfortunately i already set it to always on, so that cant be the solution. Could it be llast state?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

0 Likes
0
859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:17 AM . Last Modified: ‎2024-03-11 04:11 AM

Hi,

"Last state" may work. "Always on" should have. PowerChute runs shutdown.exe with these parameters shutdown /s /f /t %delay% /d UP:6:12 /c "PowerChute Network Shutdown has initiated a system shutdown." %delay% = 60 seconds

As with any other software once the system has been powered down the software cannot control the systems behavior. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of