Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Powerchute does not save certain values

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute does not save certain values
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Dormi98_apc
Dormi98_apc
Cadet

Posted: ‎2021-07-08 01:16 AM

0 Likes
5
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:16 AM

Powerchute does not save certain values

This was originally posted on APC forums on 8/27/2015


Hello everyone!

I got a problem with the powerchute business edition software. This is a single server environment so I am just using the Agent on the Server and the Webinterface for configuration.

System:

OS: Windos SBS 2011

SMART-UPS 3000XL connected by USB

Java 8.51

Powerchute Business Edition: 9.1.1

 

The problem is that certain values are not stored in powerchute. I can for example change the setting under "energy usage" but I cannot change other configuration items such as shutdown times. As soon as I click on the Apply Button the changed field jumps back to the previous value.
I allready tried different browsers and also tried it by using a regular workstation. No luck.
The problem was the same with an older version of Powerchute so I updated it, but still the same.

 

Any ideas?

Thanks in advance

Gerald

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • PowerChute
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:17 AM

0 Likes
0
464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:17 AM

This reply was originally posted by Bill on APC forums on 9/8/2015


Hi,

When you run the 9.1.1 or 9.2 installers they look at the UPS model and if the UPS is a SUA Smart-UPS the 9.0.3 Agent is installed. If the UPS is a SMT, SMX, or SMC Smart-UPS the 9.1.1 or 9.2 Agent is installed. This is by design. SUA model Smart-UPS communicate using a different protocol than SMT, SMX, SMCs and therefore required a different Agent.

The values you are attempting to set are stored on / saved to the UPS. The values stored on the UPS are Low Battery, OS Shutdown time, UPS turn on percent, High transfer voltage, Lower transfer voltage, Audible alarms, Perform Self-Test. If PowerChute is receiving data from the UPS (see when UPS goes on battery) the issue is with the ability to send data and have it saved.

The next time you are at the site test communication with the UPS using a different system. If you have a Windows laptop attach it and install PowerChute. Then change the settings. Another test is to uninstall PowerChute on the Windows 11 system and install APCUPSD. Using the APCUPSD configuration INI file change the settings. Then uninstall APCUPSD and reinstall PowerChute. Check the setting to see if they remained or reverted. With either test if the settings revert the issue is with the UPS.

See Answer In Context

Reply
Share
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:16 AM

0 Likes
0
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:16 AM

This reply was originally posted by Bill on APC forums on 8/27/2015


Hi,

Please provide a screen shot of the web page / setting you are experiencing the issue with. Also, what is the exact model number of the Smart-UPS? You can find the model number on the bar code sticker that will be on the back or bottom of the UPS. If the UPS has an LCD screen you ca get the model number under About "UPS Part No:".

Reply
Share
Dormi98_apc
Dormi98_apc
Cadet

Posted: ‎2021-07-08 01:16 AM

0 Likes
0
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:16 AM

This was originally posted on APC forums on 8/28/2015


I am not at the site till the middle of next week so I cannot see the label at the moment. 

Here is ascreeshot of one of the setting that I cannot change. No value here can be changed. (configure opens another page, as soon as I click apply on that one, I see this orgiginal values again)

The values in this screenshot can be changed:

Attachments
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:16 AM

0 Likes
0
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:16 AM

This reply was originally posted by Bill on APC forums on 8/31/2015


Hi,

The screenshots show that you are running PowerChute Agent 9.0.3 or older not 9.1.1. Most of the data on the configuration page gets saved to / stored on the UPS. When you run the 9.1.1 installer it looks at the UPS model and if the UPS is a SUA Smart-UPS the 9.0.3 Agent is installed. If the UPS is a SMT, SMX, or SMC Smart-UPS the 9.1.1 Agent is installed.

NOTE: You can find the Agent version information under Help – About.

  1. is the USB cable attached directly to the UPS or is the connection going through a USB hub?
  2. Does the UPS have a network management card install in it?
  3. Are there any other system attached to the UPS via serial?
Reply
Share
Dormi98_apc
Dormi98_apc
Cadet

Posted: ‎2021-07-08 01:16 AM

0 Likes
0
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:16 AM

This was originally posted on APC forums on 9/4/2015


Thanks for your inputs.

I was at the site today so I was able to identify the model: SUA3000xli

To anser your questions:

On 8/31/2015 5:41 PM, Bill said:

  • is the USB cable attached directly to the UPS or is the connection going through a USB hub?
  • Does the UPS have a network management card install in it?
  • Are there any other system attached to the UPS via serial?

1. yes directly attached - no hub

2. no

3. no

I also checked the version. You are right it is 9.0.3.604
So I uninstalled it, downloaded the new version and installed it again. It is again 9.0.3.604

I am sure that I downloaded 9.1.1. (Windows 2008 version from this site: http://www.apc.com/tools/download/software_comp.cfm?sw_sku=SFPCBE911&id=125&swfam=125) (filesize 202752KB). So how does it come that I again have 9.0.3.604 ? 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:17 AM

0 Likes
0
465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:17 AM

This reply was originally posted by Bill on APC forums on 9/8/2015


Hi,

When you run the 9.1.1 or 9.2 installers they look at the UPS model and if the UPS is a SUA Smart-UPS the 9.0.3 Agent is installed. If the UPS is a SMT, SMX, or SMC Smart-UPS the 9.1.1 or 9.2 Agent is installed. This is by design. SUA model Smart-UPS communicate using a different protocol than SMT, SMX, SMCs and therefore required a different Agent.

The values you are attempting to set are stored on / saved to the UPS. The values stored on the UPS are Low Battery, OS Shutdown time, UPS turn on percent, High transfer voltage, Lower transfer voltage, Audible alarms, Perform Self-Test. If PowerChute is receiving data from the UPS (see when UPS goes on battery) the issue is with the ability to send data and have it saved.

The next time you are at the site test communication with the UPS using a different system. If you have a Windows laptop attach it and install PowerChute. Then change the settings. Another test is to uninstall PowerChute on the Windows 11 system and install APCUPSD. Using the APCUPSD configuration INI file change the settings. Then uninstall APCUPSD and reinstall PowerChute. Check the setting to see if they remained or reverted. With either test if the settings revert the issue is with the UPS.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc