APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
Is there a list of the Windows event IDs PE can generate? I am writing a monitoring policy and have been unable to find more than a couple scattered around the web.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
I combined that with what I had and here are the results in case anyone else ever needs them. I also included the list as a spreadsheet.
Thanks for your help.
ERROR: Network connection not available, failed to connect server | 145 |
WARNING: The UPS has switched to battery backup power due to overvoltage. |
172 |
WARNING: The UPS has switched to battery backup power due to undervoltage. | 173 |
WARNING: The UPS has switched to battery backup power due to a blackout. | 174 |
WARNING: The UPS has switched to battery backup power due to a blackout | 175 |
WARNING: PowerChute causing PC to shutdown. | 176 |
WARNING: PowerChute causing PC to hibernate. |
177 |
WARNING: Battery backup providing AVR Trim (reducing the line voltage). | 203 |
WARNING: Battery backup providing AVR Boost (increasing the line voltage) | 204 |
SEVERE: Self-test failed. | 61451 |
INFORMATIONAL: Self-test passed. | 61452 |
WARNING: Battery backup transferred to battery power due to electrical noise. | 61453 |
WARNING: Battery backup transferred to battery power | 61454 |
INFORMATIONAL: Battery backup transferred to AC utility power. | 61455 |
WARNING: PowerChute not communicating with the battery backup. | 61456 |
WARNING: PowerChute not communicating with the battery backup while on battery power | 61458 |
INFORMATIONAL: Battery connected in the battery backup. | 61459 |
WARNING: Battery disconnected in the battery backup. | 61460 |
WARNING: Battery backup overloaded. | 61461 |
INFORMATIONAL: Battery backup no longer overloaded. | 61462 |
SEVERE: Battery backup failed self-test. Battery requires replacement. | 61463 |
SEVERE: PowerChute has detected an internal fault in the battery backup. | 61464 |
INFORMATIONAL: PowerChute recommenced communicating with the battery backup. | 61465 |
WARNING: PowerChute not communicating with the battery backup while on battery power. | 61483 |
INFORMATIONAL: PowerChute regained communication with the battery backup while on battery power. | 61501 |
WARNING: Internal Communication Fault with your battery backup. | 61503 |
INFORMATIONAL: Green mode is switched on for your battery backup. | 61514 |
INFORMATIONAL: Green mode is switched off for your battery backup. | 61515 |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
Hi,
There is not a list available however if you are looking to poll the log for PCPE events you can poll by source i.e. APC Data Service and APC UPS Service.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
Thanks, but I am looking for event IDs so I can monitor for them and create alerts. I could capture all the events and build a list but it could take a long time to build a complete list because a lot of events occur very rarely.
I find it incredible that a) such a list doesn't exist and b) I am the only person who wants one but apparently that's the case.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
Hi,
I found a list for you.
S.No | Event | Event ID | Event Severity |
1 | Blackout | 174 | Warning |
2 | Under voltage | 173 | Warning |
3 | Over voltage | 172 | Warning |
4 | Sensitivity fluctuation | 61453 | Warning |
5 | Self-test passed | 61452 | Information |
6 | Self-test failed | 61451 | Error |
7 | Shutdown | 176 | Information |
8 | Hibernation | 177 | Information |
9 | Online | 61455 | Information |
10 | Battery disconnected | 61460 | Error |
11 | Battery connected | 61459 | Information |
12 | UPS overloaded | 61461 | Error |
13 | UPS no longer overloaded | 61462 | Information |
13 | Loss communication | 61456 | Error |
14 | Loss communication while on battery | 61483 | Error |
15 | Gained Communication | 61465 | Information |
16 | Charger failure | 61464 | Error |
17 | AC Utility Power (AVR Trim) | 203 | Information |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
Excellent! Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
I combined that with what I had and here are the results in case anyone else ever needs them. I also included the list as a spreadsheet.
Thanks for your help.
ERROR: Network connection not available, failed to connect server | 145 |
WARNING: The UPS has switched to battery backup power due to overvoltage. |
172 |
WARNING: The UPS has switched to battery backup power due to undervoltage. | 173 |
WARNING: The UPS has switched to battery backup power due to a blackout. | 174 |
WARNING: The UPS has switched to battery backup power due to a blackout | 175 |
WARNING: PowerChute causing PC to shutdown. | 176 |
WARNING: PowerChute causing PC to hibernate. |
177 |
WARNING: Battery backup providing AVR Trim (reducing the line voltage). | 203 |
WARNING: Battery backup providing AVR Boost (increasing the line voltage) | 204 |
SEVERE: Self-test failed. | 61451 |
INFORMATIONAL: Self-test passed. | 61452 |
WARNING: Battery backup transferred to battery power due to electrical noise. | 61453 |
WARNING: Battery backup transferred to battery power | 61454 |
INFORMATIONAL: Battery backup transferred to AC utility power. | 61455 |
WARNING: PowerChute not communicating with the battery backup. | 61456 |
WARNING: PowerChute not communicating with the battery backup while on battery power | 61458 |
INFORMATIONAL: Battery connected in the battery backup. | 61459 |
WARNING: Battery disconnected in the battery backup. | 61460 |
WARNING: Battery backup overloaded. | 61461 |
INFORMATIONAL: Battery backup no longer overloaded. | 61462 |
SEVERE: Battery backup failed self-test. Battery requires replacement. | 61463 |
SEVERE: PowerChute has detected an internal fault in the battery backup. | 61464 |
INFORMATIONAL: PowerChute recommenced communicating with the battery backup. | 61465 |
WARNING: PowerChute not communicating with the battery backup while on battery power. | 61483 |
INFORMATIONAL: PowerChute regained communication with the battery backup while on battery power. | 61501 |
WARNING: Internal Communication Fault with your battery backup. | 61503 |
INFORMATIONAL: Green mode is switched on for your battery backup. | 61514 |
INFORMATIONAL: Green mode is switched off for your battery backup. | 61515 |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:08 AM . Last Modified: 2024-03-13 04:23 AM
I was also looking for this list.Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 2024-03-13 04:23 AM
Let me know if you find any errors or omissions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 2024-03-13 04:23 AM
Great work!
Many thanks.
From this thread I get that few people care WHY their UPS is eventing.
Mine did it 15 time in last 20 hours...
Having had previous HDW issues I started wondering how bad was my power furniture/voltage....
..... found this OnLine Utility by a User to get events :
http://www.seltron.net/apc/powerchute.php
Alain Charles
(hehehe - not the same Alain as previous reply - Italy here)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 2024-03-13 04:23 AM
Haha. I was about to say something about how long it took you to implement until I saw the last line of your message.
Anyway, glad it helped. If you find any errors or omissions let me know so I can update my list.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 2024-03-13 04:23 AM
Just to share some new finding:
HWinfo64 (it's a monitor) can read real-time data from APC and display it...
To monitor the "total power flowing trough the UPS" in a running graph, I'm Using MSIAfterburner with fantastic result !
But there are many other UPS info available in HWinfo64.
(HWinfo64 may pass all his data to MSIAfterburner, that allow them to be presented in a running graph)
Here is a pic from MSIAfterburner... and one from HWinfo64
In both the small arrow point to the live APC BX1400 power out.
Alain Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 2024-03-13 04:23 AM
Just checking to see how HWinfo64 as been working out for you.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.