Powerchute Network shutdown - how to power up server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute Network shutdown - how to power up server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

0 Likes
8
6173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

Powerchute Network shutdown - how to power up server

Hi,

I manage to use Powerchute Network shutdown to shutdown the server when the UPS is on battery.

However, i could not find the setting to Power up the server when the AC power is restored to the UPS.

Can you point me to the correct direction?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • PowerChute
  • Powerup
  • server
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

0 Likes
0
6171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

I know this thread is old, but I do see an issue when you have more that one server on an outlet group. If power is restored before the second server turns off during the shutdown phase, it will never turn on.

Here is an example

AC power goes off, Server 1 waits 60 minutes before shutdown and when complete, shuts off the group. Server 2 does a graceful shutdown in 5 minutes. Power is restored in 30 minutes. Server 2 never starts back up because Server 1 never went into shutdown mode.

How do you prevent this from occurring?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Sven_apc
Sven_apc
Cadet

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

0 Likes
0
6171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

I second this request!
I had a similiar situation in a productive "test" last week: power failure, PCNS started shutdown after 2 minutes (because of weak setup) but did not shutdown the UPS, as the power has been restored after 20 minutes. I have an estimated runtime of 42 minutes, so without any load it would last for days...

How do I instruct the UPS/NMC/PCNS to power on the servers after power is restored?

My servers are configured to power on after power failure, but there was no visible power failure for them - simply someone (PCNS) who requested a shutdown, which had been processed.

Thanks,
Sven

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

0 Likes
0
6173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

Hi,

PowerChute is the same as any other software application that runs on the OS. Once the OS is powered down the software ceases to run so it cannot power up the system. To have the system restart automatically you need to configure the BIOS to restart the OS when AC is restored. Then in PowerChute set it to shutdown the UPS or outlet group depending on the UPS model which will restore AC once it is returned. Kbase FA159550 discusses setting up the BIOS and PowerChute. 

What happens is when PowerChute starts the OS shutdown it commands the UPS or outlet group down. When AC is restored the UPS or outlet group wait the user defined delay and then restores AC. If AC is restored prior to the UPS or outlet group power down the system will continue with the power down, wait the defined delay and then restore AC.

If the UPS has outlet group/s you configure the actions and delays under Configuration - Outlet Groups.

If the UPS does not have outlet group/s the settings on the NMC are under Configuration - Shutdown Settings - End of Shutdown return runtime duration, return delay. See the NMC help files for assistance. 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

0 Likes
0
6172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:16 AM

Hi Bill,

I think i am near to what you are suggesting.

But i am still abit confused about the three options for the BIOS Setting.

My server was at Last State option before the outage.

When the UPS is on Battery, Powerchute shutdown my server.

But when the AC is restored, my server did not power up.

In the above scenario, should my server be power up or stay down?

My server status is on when the AC was lost, so it should be power up right?

Please advise thank you.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

0 Likes
0
6172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

Hi,

When set to last state the system should power back up. The issue may be due to Windows ACPI power management (see Kbase FA159604). If it is not that then you should contact the computer manufacture for assistance.  

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Sven_apc
Sven_apc
Cadet

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

0 Likes
0
6172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

No harry,

you have to configure your server BIOS to be "ALWAYS ON".

Because shutting down with PowerChute is identical to a normal user-initiated shutdown & poweroff. Since the UPS keeps the server power up, there is no power outage for the server, until the UPS powers off (the Outlet Group). When UPS powers on again, the server was shutdown before and restores this state (OFF).
You should be fine with "ALWAYS ON"!

And thanks Bill!
I was not sure about the fact "If AC is restored prior to the UPS or outlet group power down the system will continue with the power down, wait the defined delay and then restore AC." - I thought this would not happen and keep my servers off.

But now I only have to make sure, that everything is shutting down, then activate UPS power down and it should work. I kept this setting at "Do not turn off the UPS" because there are some other devices which I wanted to keep from power outages if possible.
(i.e. a Tape Library that needs ages after power on)
As I don't have different Outlet Groups, I have to power off everything off and then on again.

Thanks for explanation!


Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

0 Likes
0
6172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

Hi 

I am having the same problem, but with apcupsd running on ubuntu 16.04

No restart after power is back

Bios set to always on.

Did read somewhere that ups has to shut down via killpower . Not sure if this is happening.

How can I ensure  powering back up?

tanks for the help

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

0 Likes
0
6172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

Hi,

This post does not belong here. This thread is about PCNS not APCUPSD. 

To answer your question, yes the UPS must power down to allow the BIOS to see that power has been restored to restart. I know when running apcupsd on Windows you must configured killpower. I assume you must do the same when running on ubuntu but you should post your inquiry to the apcupsd email list http://www.apcupsd.org/wordpress/support/

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

0 Likes
0
6172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-13 01:15 AM

I know this thread is old, but I do see an issue when you have more that one server on an outlet group. If power is restored before the second server turns off during the shutdown phase, it will never turn on.

Here is an example

AC power goes off, Server 1 waits 60 minutes before shutdown and when complete, shuts off the group. Server 2 does a graceful shutdown in 5 minutes. Power is restored in 30 minutes. Server 2 never starts back up because Server 1 never went into shutdown mode.

How do you prevent this from occurring?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of