Powerchute Business adition question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute Business adition question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

0 Likes
5
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

Powerchute Business adition question

Dear friends,

I want to buy the APC Smart-UPS SC 420VA 230V.

My questions are:

1. Will it work with powerchute business edition?

2. I want to be sure that if the elctricity is down for long time and the ups is off, when the power comes back the ups will open automiatically. Can someone please verify this?

Thank you very much

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

Thank you so much for your answers!

I just contacted WILO, so when they answer i will get back on you with their answer.

Thanks again!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

Hi,

Yes, Smart-UPS SC products are designed to use PowerChute Business Edition.

And yes, this and most UPS models will always turn on when AC power returns if it was shutdown due to a low battery and this would be the default. Some UPSs, specifically when told to shutdown by software like PowerChute (rather than turning off because the battery was depleted), can be programmed to turn off and stay off but this is not the default behavior and would have to be modified by the user in software.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

Thanks so much for the answer!

So i go for the APC Smart-UPS SC 420VA 230V!

My purpose of buying this ups is that i just installed a tisun solar station on my roof. It warms a special liquid with the help of the sun and then this liquid is moved inside tubes to a big boiler.

The movement of the liquid is made by a wilo motor http://productfinder.wilo.com/en/GR/product/00000000000179fe0001003a/fc_product_datasheet

This motor as you can see has a maximum power consumption of 63 watts.

The main problem is that this motor should always be on, or at least be off for the less time.

Can you please assure me that even if the electricity goes down for long time, then the ups will start automatically when the power is back on , and the motor will start again?

Thanks so much for the support!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

Hi,

Smart-UPS SC are not designed to work with motors. The UPS while on battery outputs a step-approximated sign wave. This waveshape, while okay for computer-type equipment, is not particularly compatible with most motor loads. The result may be that motors run very slowly, erratically, or not at all when the UPS is on battery.

To protect your equipment, we recommends first determining the appropriate size UPS for the motor load in question. Ensure that the Volt Amp rating of the UPS is sufficient to handle the start-up inrush current draw of the motor. Secondly, select a UPS which outputs a Pure Sine Wave when on battery, such as a Smart-UPS SMT750.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

Hello,

I can just assure you of how the UPS operates by default. Yes, it is designed to turn back on automatically when AC power comes back after the UPS has previously turned off due to discharged battery. This happens by default even if you don't use PowerChute at all.

While the power consumption of the motor is low and the amperage is low according to that data sheet, have you tried to contact the motor vendor on what they recommend for a UPS?

Because it is a "motor" of sorts, sometimes motors cause a lot of in rush current (which I don't think is the case here), or they cannot do well with a step approximation to a sinewave like this UPS has. I would just want to ask the vendor if they know anything about that and if a pure sinewave UPS is required. The problem could be that when the UPS goes to battery power - which is when this UPS will output a step approximated sinewave - the motor could have a problem accepting that and reboot or not operate at all. I don't want you to be disappointed if you see an issue like this without checking on it first. It may not be an issue at all.

If there is a problem, you'd want to look at a pure sinewave UPS such as the SC's replacement - SMC, or something with SMX/SMT prefix. We have a knowledge base here that talks about these issues a little bit and I just wanted to share with you for reference -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA158851 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:21 AM . Last Modified: ‎2024-02-29 11:13 PM

Thank you so much for your answers!

I just contacted WILO, so when they answer i will get back on you with their answer.

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore