We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-29 04:00 AM . Last Modified: 2024-03-13 01:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:00 AM . Last Modified: 2024-03-13 01:55 AM
We have a Smart UPS 3000.
Installed the BE server and agent on a 2003 server which is connected to UPS through USB cable.
We have 4 other servers to connect (communication for shutdown purposes) to this UPS.
When I try to install the agent on other servers it asks for communication options. What does this mean? According to my understanding main BE server is connected to UPS through USB. The agent on another server should connect to server rather than the UPS itself.
On another server what i did was select usb communication setting to finish installation of agent. But when I try to add this server to the device list, i can see it there but while adding it there is an error. I am not sure if communication is happening between BE server and this agent.
Kindly help.
Nitin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:01 AM . Last Modified: 2024-03-13 01:55 AM
Nitin,
For you to be able to install PowerChute Business Edition Agent, it needs to be connected directly to the UPS via the USB or Serial cable. PCBE Agent communicates thru this method in order for it to manage and control the UPS. Unfortunately you can only use one method/cable at a time. If you are using an SU or SUA SmartUPS you can purchase an Interface Expander or Share-UPS so that you could have more serial ports available.
For a PCBE Agent to be added or communicate to the PCBE Server, a network should be present. PCBE Agent, Server and Console communicates through the network.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:01 AM . Last Modified: 2024-03-13 01:55 AM
Nitin,
For you to be able to install PowerChute Business Edition Agent, it needs to be connected directly to the UPS via the USB or Serial cable. PCBE Agent communicates thru this method in order for it to manage and control the UPS. Unfortunately you can only use one method/cable at a time. If you are using an SU or SUA SmartUPS you can purchase an Interface Expander or Share-UPS so that you could have more serial ports available.
For a PCBE Agent to be added or communicate to the PCBE Server, a network should be present. PCBE Agent, Server and Console communicates through the network.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of