Powerchute Business 9.x shutdown command line doesn´t work

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute Business 9.x shutdown command line doesn´t work
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:44 AM

0 Likes
4
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:44 AM

Powerchute Business 9.x shutdown command line doesn´t work

Hi,

I´m running pcb 9.x on a windows server. The UPS is Samrt UPS 750. It´s connected via serial Cable an works fine. What I ant to do is the following:

I want to shut down plink.exe (ssh) an synology disk station in case of power failure. When I start the executable from the command line: C:\plink.exe -ssh -pw passwortdiskstation root@192.168.8.6 poweroff The Synology Disk Station powers off. The Problem is: I can´t do this in PCB. When testing the Command line, nothing happens. I´ve also tried this:

3. If the test fails, go to Services and right click on the Agent service and choose Properties.

4. Click on the "Log On" tab.

5. Check the box for "Interact with Desktop". 

When I do this, communication between server and upc is lost.

Any Idea?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

I think I got it going like Kenneth...;)

Thanks a lot!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2025-05-27 11:09 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2025-05-27 11:09 PM

Hi,

The issue may be resolved by adding @start to the command line as listed in FAQ FA168226 . If that does not resolve the issue the cause most likely is due to PCBE is a service and ever since Windows Vista was release anytime a service attempts to run an executable it must be started in session zero. More information on session zero is noted in FAQ FA168226 .

there are a few post here that discuss work arounds. I suggest reviewing Kenneth's post dated 26 April 2015 

http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/3033/pcb-sh...

There is another work around listed in this post 

http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/12714/-fyi-...

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:44 AM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:44 AM

Hi Bill,

I´ll check this out. May take some time. Will be back as soon I´ve tried out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:44 AM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:44 AM

Hi Bill,

I´ve taken a closer look to Kenneth´s post dated 26 April 2015.

"

I'm late to this party, but I encountered the exact same problem and figured out a work-around: use the Windows Task Scheduler!

  1. Create a task that executes whatever you'd like (I tested with shutdown /i), set a suitable user account for running it (I picked my user account) and check "Run with highest privileges" if necessary (not necessary for my test), and allow it to be started manually. Give the task a suitable name, e.g. ShutdownTest.
  2. Create a script for PowerChute to execute, and add this line: @start schtasks /run /tn ShutdownTest
  3. Execute it from PowerChute and watch it work ;)"

 

I´ve tried to Create an new Scheduled Task with the GUI Scheduled Task planer. I wasn´t able to find the option "start manually". As far as I´ve understood I have to add this line "@start schtasks /run /tn ShutdownTest" to my existing cmd file for getting scheduled task planer into interaction with the cmd file.

Question: How do I do this in conrete?;)

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

I think I got it going like Kenneth...;)

Thanks a lot!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore