Powerchute 3.01 with two ESXi 4.1 hosts not shutting VMs in power failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute 3.01 with two ESXi 4.1 hosts not shutting VMs in power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:38 AM

0 Likes
3
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:38 AM

Powerchute 3.01 with two ESXi 4.1 hosts not shutting VMs in power failure

I am running Powerchute pcns 3.01 on Vma connecting to two ESXi 4.1 hosts and connecting to a APC 750XL UPS with a network card. There seems to be a disconnect between the power loss failure and the shutdown command. Is there any way to test this process without actually shutting down all my servers?

The last power failure gave me this log file info:

750XL log:
09/08/2012 14:07:36 UPS: A discharged battery condition no longer exists.
09/08/2012 13:49:03 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/08/2012 13:48:50 System: Network service started. System IP is 10.1.1.204 from manually configured settings.
09/08/2012 13:49:02 UPS: Restored the local network management interface-to-UPS communication.
09/08/2012 13:48:49 System: Coldstart.
09/08/2012 12:44:55 UPS: A low battery condition no longer exists.
09/08/2012 12:44:55 UPS: The output power is turned off due to a low battery.
09/08/2012 12:42:21 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
09/08/2012 12:12:55 UPS: On battery power in response to an input power problem.

vMA log:
09/08/2012 15:08:33 Available runtime is sufficient.
09/08/2012 15:07:55 Battery has recharged
09/08/2012 14:57:32 Available runtime has been exceeded.
09/08/2012 14:57:14 PowerChute successfully opened TCP port 6547.
09/08/2012 14:57:11 PowerChute successfully opened TCP port 3052.
09/08/2012 14:57:07 PowerChute Network Shutdown version 3.0.1 started
09/08/2012 14:57:06 PowerChute successfully opened UDP port 3052.
09/08/2012 14:57:02 Battery is discharged
09/08/2012 14:57:02 Communication has been established
09/08/2012 13:13:01 UPS has switched to battery power
09/08/2012 12:28:21 Input power has been restored: UPS has switched to On Line operation
09/08/2012 12:28:19 UPS has switched to battery power

Thanks in advance,
Chris

Message was edited by: HorizonsAdmin

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 3.01
  • esxi
  • hosts
  • management
  • pcns
  • PowerChute
  • server
  • vm
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

can you provide the data log too please? under logs->data->log?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

hi Chris,

can you give me the data log from this time too from the network management card in the UPS?

have you done any specific configuration on the PCNS installed on the vMA? or did you just install it and thats it?

are these times lined up or are they really skewed and thats part of the problem?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

Here are the complete logs from the 750XL log:
09/08/2012 14:07:36 UPS: A discharged battery condition no longer exists.
09/08/2012 13:49:03 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/08/2012 13:48:50 System: Network service started. System IP is 10.1.1.204 from manually configured settings.
09/08/2012 13:49:02 UPS: Restored the local network management interface-to-UPS communication.
09/08/2012 13:48:49 System: Coldstart.
09/08/2012 12:44:55 UPS: A low battery condition no longer exists.
09/08/2012 12:44:55 UPS: The output power is turned off due to a low battery.
09/08/2012 12:42:21 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
09/08/2012 12:12:55 UPS: On battery power in response to an input power problem.
09/08/2012 11:43:41 System: Web user 'apc' logged out from 192.168.10.1.
09/08/2012 11:40:40 System: Web user 'apc' logged in from 192.168.10.1.
09/08/2012 11:28:15 UPS: No longer on battery power.
09/08/2012 11:28:12 UPS: On battery power in response to an input power problem.

Yes, the difference in the times seems to be the problem. It looks to me like there was a half hour between the power down event and the response from the hosts to shut down. I followed the "How to install PowerChute Network Shutdown 3.0 on VMware ESXi – vMA 4.0, 4.1, 5.0". The only configuration that I did after installation was to add an additional server to the list via "sudo vifp addserver"

Thanks,
Chris

Message was edited by: HorizonsAdmin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:30 AM . Last Modified: ‎2024-03-06 01:37 AM

can you provide the data log too please? under logs->data->log?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.