Powerchute 3.0.1 and ESX 4.1 & 5.1 host

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute 3.0.1 and ESX 4.1 & 5.1 host
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:13 PM

0 Likes
7
2032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:13 PM

Powerchute 3.0.1 and ESX 4.1 & 5.1 host

I'm having the same issue I've seen floating around for a few other people, I'm able to get VM shutdowns to work in any order I want through a shell script, but the ESXi hosts I have this installed on won't work.

I've tested this on both ESXi 4.1 & ESXi 5.1 servers and I'm experiencing the same issue with PowerChute 3.0.1. Some are HA, and some are just regular standalone hosts, so it seems to be something other than the version of ESXi host causing the issues. One thing that does tie across all hosts is that they have symbols in their passwords, not sure if that would make a difference.

I've verified that all hosts and vCenter are licensed.

The host is added using vifptarget -s (vMA host always last in the list)

The host returns all NIC info from vicfg-nics --list command

I've added the export PERL_LWP_SSL_VERIFY_HOSTNAME=0 command to my shutdown script per FA159783

I don't believe this is the DNS issue in FA166844, since vifp listservers shows me the ESX hosts IP, not DNS name.

Again, VMs shut down without issue in whatever order I prefer, just the hosts I'm having issues with.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • powerchute_network_shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

0 Likes
0
2032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

Hi,

You can test PowerChute shutdown of the host manually. CD to /opt/APC/PowerChute/group1 (this is assuming app is installed to the default path) The command is sudo bin/shutdown If that does not work you can run the shutdown in debug mode by editing /opt/APC/PowerChute/group1/bin/shutdown (the instruction for editing the script are included in the file).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:13 PM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:13 PM

Hi,

PCNS 3.0.1 uses VIFPTARGET/vMATarget functionality provided by the vMA to store the ESXi host credentials. PCNS retrieves the credentials when connecting to the host to shut it down using the RCLI/Perl SDK. These credentials are actually stored in an XML file on the vMA. When you add a target host using the vifp addserver command a new accounts is created. We use the same file / grab the same info when running shutdownvms.sh

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

Again, thanks for the clarification Bill.

So I tested just running the shutdown script in /opt/APC/PowerChute/group1/bin/ and was getting the following error

1116_error.JPG

So I made a backup of shutdown, and changed the line inside the script from:

perl ./bin/shutdownhost.pl --operation shutdown --username xxxxx --password xxxxx --loglevel debug

to

perl ./shutdownhost.pl --operation shutdown --username xxxxx --password xxxxx --loglevel debug

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

Hi,

You received that error because you were attempting to run the shutdown file from within /opt/APC/PowerChute/group1/bin If you want to test the file without editing it you should cd to /opt/APC/PowerChute/group1 and then type sudo bin/shutdown

By editing the file as you have PowerChute will not shut the host down properly. You need to put the file back to its original content!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

Thanks Bill,

Yea in testing the script worked, but actually initiating a PowerChute shutdown still didn't shut down the hosts. I've recovered the original shutdown file so it should be default again. Where are the verbose logs stored for the shutdown file in /opt/APC/PowerChute/group1/bin/ ? I've specified the --loglevel debug in shutdown and I'd like to see exactly why these hosts still aren't restarting.

Thanks,

Marcus

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

Marcus,

PCNS does not restart the host. If you want the host to restart you would need to configure that in the BIOS.

As for the debug log it is put in /tmp

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

I'm having the same issue I've seen floating around for a few other people, I'm able to get VM shutdowns to work in any order I want through a shell script, but the ESXi hosts I have this installed on won't work.

I've tested this on both ESXi 4.1 & ESXi 5.1 servers and I'm experiencing the same issue with PowerChute 3.0.1. Some are HA, and some are just regular standalone hosts, so it seems to be something other than the version of ESXi host causing the issues. One thing that does tie across all hosts is that they have symbols in their passwords, not sure if that would make a difference.

I've verified that all hosts and vCenter are licensed.

The host is added using vifptarget -s (vMA host always last in the list)

The host returns all NIC info from vicfg-nics --list command

I've added the export PERL_LWP_SSL_VERIFY_HOSTNAME=0 command to my shutdown script per FA159783

I don't believe this is the DNS issue in FA166844, since vifp listservers shows me the ESX hosts IP, not DNS name.

Again, VMs shut down without issue in whatever order I prefer, just the hosts I'm having issues with.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:57 AM . Last Modified: ‎2024-03-05 11:12 PM

Hi,

You can test PowerChute shutdown of the host manually. CD to /opt/APC/PowerChute/group1 (this is assuming app is installed to the default path) The command is sudo bin/shutdown If that does not work you can run the shutdown in debug mode by editing /opt/APC/PowerChute/group1/bin/shutdown (the instruction for editing the script are included in the file).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore