PowerChute cannot communicate with the Management Card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute cannot communicate with the Management Card
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

0 Likes
2
4530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

PowerChute cannot communicate with the Management Card

Hello All,

Since the installation of the Network Shutdown could not make the software synchronizes with the network card I have in the UPS Smart-UPS 3000 RM with AP9617 network card.
Deputy mistakes I have at this moment, someone may help me?

Thank you very much

Message was edited by: Giux

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

0 Likes
0
4530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

In addition to what Eramus said, I would like to add some more points. It appears that the PCNS authentication phrase does not match up with the NMC auth. phrase. The default administrator authentication phrase used by PowerChute Network Shutdown is: admin user phrase. If you change the Authentication Phrase, you must also change it on the Web Management Card. Otherwise, PowerChute Network Shutdown and the Web Management Card will not be able to communicate.

The Web Management Card Administrator User Name and Authentication Phrase must be the same as those used by PowerChute Network Shutdown. Set these parameters in the Web Management Card user interface by using the User Manager page, selected from the System menu or in later firmware revisions (above 3.X) in the menu UPS -> PowerChute -> Configuration -> Authentication Phrase.

If this does not work, then I recommend you to reset the NMC settings to its factory defaults except TCP/IP under Administration. And then reinstall the PCNS software and check if it communicates with the NMC.

I hope that this helps.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

0 Likes
0
4530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

Read through the following APC K-Bases for more information and troubleshooting steps on this problem:

For advice on DHCP-based [communication loss|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=443]

For many other general troubleshooting steps, check here

Also be sure to verify the [system requirements|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2910] for PCNS.

Edit: On the off-chance these links don't work for you, you can find them in our Knowledge Base section on our website. The numbers from first to last for each document respectively are: 443, 7711, 2910.

Message was edited by: Erasmus

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

0 Likes
0
4531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:36 AM . Last Modified: ‎2024-02-14 11:37 PM

In addition to what Eramus said, I would like to add some more points. It appears that the PCNS authentication phrase does not match up with the NMC auth. phrase. The default administrator authentication phrase used by PowerChute Network Shutdown is: admin user phrase. If you change the Authentication Phrase, you must also change it on the Web Management Card. Otherwise, PowerChute Network Shutdown and the Web Management Card will not be able to communicate.

The Web Management Card Administrator User Name and Authentication Phrase must be the same as those used by PowerChute Network Shutdown. Set these parameters in the Web Management Card user interface by using the User Manager page, selected from the System menu or in later firmware revisions (above 3.X) in the menu UPS -> PowerChute -> Configuration -> Authentication Phrase.

If this does not work, then I recommend you to reset the NMC settings to its factory defaults except TCP/IP under Administration. And then reinstall the PCNS software and check if it communicates with the NMC.

I hope that this helps.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of