PowerChute can't find Smart-UPS 3000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute can't find Smart-UPS 3000
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:20 AM

0 Likes
4
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:20 AM

PowerChute can't find Smart-UPS 3000

We have a Smart-UPS 3000 RM XL with a AP9619 Network Management Card EM installed. I want to run a script from a networked computer that is triggered by an event from the UPS that will shutdown our servers. First I tried to install PowerChute Network Shutdown 2.2.1 Build 12 but the software "cannot communicate with the Management Card". I can log into the management card and it can be pinged from the computer that has PowerChute installed. The UPS is also able to send out it's self test e-mails. There is no firewall installed on the running PowerChute. Also, I have verified the username, password and pass phrase on both the UPS and in PowerChute several times.

As a test I also installed APC PowerChute Business Edition Basic on another computer to see if it could see the UPS and it could not.

Finally, we also have a Symmetra LX 16000 RM with an AP9619 Card and it is working fine with Network Shutdown.

Any help would be appreciated. Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

0 Likes
0
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

We have a Smart-UPS 3000 RM XL with a AP9619 Network Management Card EM installed. I want to run a script from a networked computer that is triggered by an event from the UPS that will shutdown our servers. First I tried to install PowerChute Network Shutdown 2.2.1 Build 12 but the software "cannot communicate with the Management Card". I can log into the management card and it can be pinged from the computer that has PowerChute installed. The UPS is also able to send out it's self test e-mails. There is no firewall installed on the running PowerChute. Also, I have verified the username, password and pass phrase on both the UPS and in PowerChute several times.

As a test I also installed APC PowerChute Business Edition Basic on another computer to see if it could see the UPS and it could not.

Finally, we also have a Symmetra LX 16000 RM with an AP9619 Card and it is working fine with Network Shutdown.

Any help would be appreciated. Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:20 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:20 AM

Hello,

Are you using PowerChute Business Edition and Network Shutdown in conjunction? Also, if there is a Network Management Card in the UPS, then Business Edition will not operate correctly. When PowerChute Network Shutdown is installed on a box and cannot talk to the Network Management Card, 95% of the time it is because the username, password, and authentication phrase has been altered, or there is some firewall or antivirus software blocking port 3052. What OS is the PCNS client running on? If it is windows, can you run netstat -a to verify port 3052 is open and running? What is the firmware on the Network Management Card? Are you running two PowerChute Network Shutdown clients on the same computer?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

PowerChute and Network Shutdown have not been installed on the same computer. I had installed each application on separate computers. I have now uninstalled Network Shutdown. I have tried to run PowerChute from a Windows XP workstation and a Windows 2003 R2 server. Each time while the software is installing I get:

Registering with Management Card(s)
Please wait.
Gathering Management Card addresses
Connecting to Management Card(s)
Sending registration to Management Card(s)
Verifying communication with Management Card(s) . . .
Registration Results:

192.168.1.25 communicated successfully

Click Next to continue.

(I'm not sure what is going on with this webpage but it is omitting "192.168.1.25 communicated successfullly" from below Registration Results in the message above. I can see it in the edit window but not in the post?)


The above appears to indicate that PowerChute can connect to the management card but still no joy. I have verified the username, password and changed the pass phrase on both the UPS and in PowerChute several times too.

When I run netstat –a I get the following for port 3052:

TCP computername:3052 computername.domainname:0 LISTENING
UDP computername:3052 *:*

There is no third party firewall installed on the server and the Windows firewall has been disabled. We use Sophos anti-virus. Sophos is installed on another computer running PowerChute that has no problem communication with our Symmetra LX 16000 RM. Sophos does not have any firewall/malware functionality build into it.


I’m not sure how to tell the firmware of the management card. The only reference to firmware I can find looks like it is for the UPS itself. We have a Smart-UPS 3000 RM XL with Firmware Revision 691.16.D

Thank you very much for helping me with this!

Message was edited by: akbrew

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

akbrew,
I'm not sure if youa re still working on geting PCNS to communicate with your network management card, but if you are, you should log into the netowrk management card and see if the powerchute software registered itself with the card. This can be verified by finding the IP address of the PowerChute client computer in teh list of PowerChute IP addresses in the UPS -> PowerChute menu of the managmenet card's interface. If you have uninstalled the software since your last try, you would have to reinstall it. If your computer's IP is not listed on the management card, you can add it manually.

If you are still having problems communicating after either verifying that the IP address is properly listed in the management card interface, or adding it manually, you might want to reset the card to its factory defaults, and try the installation again without MD5 encryption enabled on the card. If it works without MD5, try using a different phrase.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

0 Likes
0
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:19 AM . Last Modified: ‎2024-03-08 12:19 AM

We have a Smart-UPS 3000 RM XL with a AP9619 Network Management Card EM installed. I want to run a script from a networked computer that is triggered by an event from the UPS that will shutdown our servers. First I tried to install PowerChute Network Shutdown 2.2.1 Build 12 but the software "cannot communicate with the Management Card". I can log into the management card and it can be pinged from the computer that has PowerChute installed. The UPS is also able to send out it's self test e-mails. There is no firewall installed on the running PowerChute. Also, I have verified the username, password and pass phrase on both the UPS and in PowerChute several times.

As a test I also installed APC PowerChute Business Edition Basic on another computer to see if it could see the UPS and it could not.

Finally, we also have a Symmetra LX 16000 RM with an AP9619 Card and it is working fine with Network Shutdown.

Any help would be appreciated. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of