Posted: 2021-07-08 05:27 AM
This question was originally posted by Fabio on APC forums on 7/20/2018
Hello,
I will soon install SRT3000xli + 2 battery pack SRT96BP + AP9631. I have a question about PowerChute behaviour during calibration. How it will consider the status of UPS? It will see that UPS is "on battery"? If I set a delay time for "UPS on battery" event, will PowerChute shutdown the system even if there is no AC fault? I would like to avoid that PCNS will shutdown the servers during calibration.
Thanks!
Posted: 2021-07-08 05:28 AM
Posted: 2021-07-08 05:28 AM
This reply was originally posted by Bill on APC forums on 7/20/2018
Hi,
PowerChute Network Shutdown will not react to a runtime calibration test being performed on the UPS.
Posted: 2021-07-08 05:28 AM
This reply was originally posted by Fabio on APC forums on 8/1/2018
Thank you!