Hello,
I will soon install SRT3000xli + 2 battery pack SRT96BP + AP9631. I have a question about PowerChute behaviour during calibration. How it will consider the status of UPS? It will see that UPS is "on battery"? If I set a delay time for "UPS on battery" event, will PowerChute shutdown the system even if there is no AC fault? I would like to avoid that PCNS will shutdown the servers during calibration.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 05:28 AM . Last Modified: 2024-02-15 12:18 AM
Hi,
PowerChute Network Shutdown will not react to a runtime calibration test being performed on the UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 05:28 AM . Last Modified: 2024-02-15 12:18 AM
Thank you!