PowerChute Personal Edition 3.0.2 install error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Personal Edition 3.0.2 install error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-03-12 07:09 AM

0 Likes
13
2915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-03-12 07:09 AM

PowerChute Personal Edition 3.0.2 install error

Hello. I have a Back-UPS ES700 on my system.

A week ago, the software began to produce an error about the faulty service. I deleted this software today and tried to install it again, and now I'm having trouble installing it. I tried all the solutions to eliminate similar errors from the site of the APC, but nothing helped.
Here is a screenshot of the error and information about the USB device.

Install Error

 

USB-dev

 

On rus installer - error about Windows Installer (i don`t know why).

 

UPD:

Tried to establish Buissness Edithion. Installation is normal, the device is located on one of the USB ports but when trying to apply configuration on it the following error occurs:

Config Fail

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

Hello. I switched to WINDOWS 10 and my problem with APC was decided. The program is quietly installed and works.
It turns out the case was in my last OS, probably with the damaged .net framework. I'm glad that my APS is working.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2025-05-27 10:32 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2025-05-27 10:32 PM

Hi Klaus,

PowerChute Business edition software is not compatible with backups products. The compatible one is Powerchute Personal edition. As there is an issue in the Powerchute Personal edition software while installing I would suggest you reset the UPS by performing a brain dead. Before performing the brain dead please remove the USB cable. Once the test is done reconnect the USB cable and install Powerchute Personal edition software. For your reference, I am providing the link to download the Powerchute Personal edition software.

Link: https://www.se.com/us/en/product-range/61934-powerchute-personal-edition/#overview

 

Here is the procedure to perform a brain dead test.

1. Disconnect any attached load from the unit.

2. Unplug the UPS from the wall socket.

3. Disconnect the UPS' internal battery.

4. Push and hold the "On" button on the UPS for 5 seconds

5. Reconnect internal battery.

6. Plug UPS in to a known good power source.

7. Turn UPS on. 

If the issue still persists please get back to me with the screen shot of the error, model number of the ups which is on white bar code label and also the operating system of your computer?

Regards,

Vinay

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-03-12 07:23 AM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-03-12 07:23 AM

Hi. Thx for answer. 

Brain dead test doesn`t help.

Again same error:

 

Model of UPS: BE700G-RS

O/s: Win7 x64

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

Hi,

Please send a screenshot of the loaded drivers. See example below. I would like to see what is displayed under the heading of Batteries and also under Human Interface Devices. To access these open Control Panel and select Device Manager

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-03-12 07:15 AM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-03-12 07:15 AM

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:19 PM

Hi,

Please changed the driver to HID UPS (see FAQ 159743). Then disconnect the USB cable and verify the drivers are removed from the list. Once they have been removed attached the USB cable and verify the HID UPS driver is loaded under battery and that American Power Conversion UPS is re-added to Human Interface Devices. Once the drivers are reloaded run the installer. The UPS should be discovered and the APC UPS driver should re-load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-03-12 07:16 AM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-03-12 07:16 AM

Hello.

Okay i just change driver like in FAQ and drivers are gone with UPS plugged to my PC.

And same error again. Mb my USB PC-to-UPS cable is broken or something?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:19 PM

Hi,

I do not think it is a cable issue since the drivers load when the cable is attached. It may be an issue with the bus blocking the software from finding the UPS. Take a look at FAQ FA283181 and test the communications using USBDEVIEW.exe. When running UASBDEVIEW.exe look to see if the UPS is discovered and that the serial number is displayed. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:19 PM

I need to make and send you this file?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

Hi,

I do not need to see the file. Does USBDEVIEW.exe show that that UPS is connected and does it display the serial number? If it does than I cannot say why PCPE will not discover the UPS. If is does show the UPS and serial number I suggest installing APCUPSD and use that software as your shutdown software. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-03-12 07:19 AM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-03-12 07:19 AM

Yes it does

 

And link to APCUPSD seems broken?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

Hi,

enter apcupsd.org to gain access to the site. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

0 Likes
0
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

Okay. Manual install drivers in apcupsd folder and my UPS works with this APCUPSD software. Better than nothing i guess? Anyway thanks for help. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Klausbarka_apc
Crewman Klausbarka_apc
Crewman

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

0 Likes
0
2914
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:06 AM . Last Modified: ‎2024-02-29 10:18 PM

Hello. I switched to WINDOWS 10 and my problem with APC was decided. The program is quietly installed and works.
It turns out the case was in my last OS, probably with the damaged .net framework. I'm glad that my APS is working.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of