PowerChute PE does not shut down WHS 2011

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute PE does not shut down WHS 2011
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
9
2115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

PowerChute PE does not shut down WHS 2011

I just purchased a BE550G. I've installed PowerChute Personal Edition 3.0.2 on my Windows Home Server 2011 box and the UPS is plugged in via USB.

I have set PCPE to "preserve battery power" and shut down after 4 minutes.

When I run a test by unplugging the UPS, the "time until shutdown" counts down appropriately from 4 minutes to 1 minute. Then it goes to "<1 minute" and stays there. I ran a stopwatch and it sat there at "<1 minute" for 5 minutes without doing anything. Total time on battery was almost 10 minutes before I plugged the UPS back in.

What's going on here?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

Any ideas?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

We actually just had a blackout, and it looks like my PC went into sleep mode 4 minutes after the power went down. I assume the fact that I was logged in via RDP prevented it from going to sleep.

I don't want it to go to sleep though. I want it to actually shut down. I don't see an option for that in PCPE.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

This thread might help - http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/4171/940-0272a-as-rs232/1#24...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

Ahh I think I see. I disabled hibernation using "powercfg -h off" and will see if that solves the problem. I'll update tonight when I get home. Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

Looks like that worked! Thanks.

Now I'm puzzling over how the UPS turns the PC back on after regaining power.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

>
My BIOS is set up to bring the PC back to the last power state upon power restoration.

That shouldn't come into play though. PowerChute initiates a complete shutdown, bringing the power state of the PC to off. The UPS maintains power to the plug continuously. So when the UPS is plugged back in, how does the PC get turned on?
>

The UPS will cycle the output power off and then on to turn the computer back on.

It will only do this after PowerChute tells the UPS that it is shutting down the computer, and after the computer has had enough time to safely shut down.

If you unplug the USB cable, PowerChute will not shut down the computer and the UPS will stay on until the battery is depleted.

>
The PC did in fact turn back on when I plugged the UPS back into the wall, despite the fact that the UPS had plenty of battery left and the PC was fully shut down.
>

Sounds like the system worked.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

Ah, I didn't realize the UPS will cycle the power. It makes sense now.

Yes, the system is working to my satisfaction now. Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

You'll need to setup your computer BIOS to wake up the PC when power gets restored. You can view an article from our FAQ/KBase to learn more about it, I have posted the link below. Once you are on the FAQ page, search for FA159550.

[APC FAQ|www.apc.com/site/support/index.cfm/faq/]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

My BIOS is set up to bring the PC back to the last power state upon power restoration.

That shouldn't come into play though. PowerChute initiates a complete shutdown, bringing the power state of the PC to off. The UPS maintains power to the plug continuously. So when the UPS is plugged back in, how does the PC get turned on?

Note that I expected the PC to stay off when I plugged the UPS back in After all, how would the PC even know? The PSU sees continuous power throughout the whole process. Maybe it powers on via USB? I'll have to check the BIOS settings to see if there's something about that.

The PC did in fact turn back on when I plugged the UPS back into the wall, despite the fact that the UPS had plenty of battery left and the PC was fully shut down.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

0 Likes
0
2115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:57 AM . Last Modified: ‎2024-03-06 12:04 AM

Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore