PowerChute Network Shutdown 4.2.0 Build 6729 Shuts Down Host OS following Reboot?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown 4.2.0 Build 6729 Shuts Down Host OS following Reboot?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:44 PM . Last Modified: ‎2024-03-12 01:10 AM

0 Likes
1
605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:44 PM . Last Modified: ‎2024-03-12 01:10 AM

PowerChute Network Shutdown 4.2.0 Build 6729 Shuts Down Host OS following Reboot?

We have an HP Proliant Server that is used to host a Hyper-V Virtualised System.

I have just installed updates on 4 Windows Guests and successfully rebooted each in turn to complete the upgrade process.  BUT I had a problem with the Host OS (Windows 2008 R2) - following the upgrade I got the following events in the event log followed by a shutdown;

09/29/2017 22:50:56 Available runtime has been exceeded.
09/29/2017 22:50:56 Communication has been established.

There are no events on the UPS Network Management Card 2?

This is the third system I have had this problem with.

Does anyone have a solution to this problem other than to disable the "Available runtime has been exceeded" event?
 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:44 PM . Last Modified: ‎2024-03-12 01:10 AM

0 Likes
0
605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:44 PM . Last Modified: ‎2024-03-12 01:10 AM

Hi,

Sorry for the inconvenience. Available runtime has been exceeded is discussed on page 78 of the PowerChute Network Shutdown Hyper-V User's Guide. http://www.apc.com/salestools/PMAR-9E5LP4/PMAR-9E5LP4_R3_EN.pdf?sdirect=true

In Schneider Electric FAQ FA241713 "PowerChute Network Shutdown reports "Available runtime has been exceeded" and by clicking on help in the PowerChute web interface.

I cannot be sure with out seeing he pcnsconfig.ini and the NMC config.ini however in 99% of cases you need to increase the low battery threshold in the NMC to be 2 minutes greater that need needed time for PowerChute to shutdown the OS. The NMC ships with the low battery threshold default of 2 minutes PowerChute needs a minimum of 4 minutes (greater when powering down VMs) so by increasing the low battery threshold in the NMC to 4 minutes the error will be resolved. 

Below is the text from the FAQ

Issue:
PowerChute Network Shutdown reports "Available runtime has been exceeded". and or PowerChute shuts down OS due to "Available runtime has been exceeded"

Product:
PowerChute Network Shutdown versions 3.1, 4.x

Environment:
All supported OS

Cause:
Condition 1 for all configurations except VMware and Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Condition 2 for all configurations except VMware and Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

For  conditions 3 and 4 below, the "total shutdown time" includes the following durations:

  • VM migration duration
  • VM shutdown and startup duration
  • vApp shutdown and startup duration
  • Shutdown command file duration
  • Built-in duration of 2 minutes (this consists of a 10 second OS shutdown duration and a 60 second OS shutdown duration; rounded up)

The event occurs with either of the following conditions:

Condition 3 for VMware:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Condition 4 for VMware:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

For conditions 5 and 6 below, the "total shutdown time" includes the following durations:

  • VM migration duration - Hyper-V only
  • VM shutdown and startup duration- Hyper-V only
  • Host Maintenance duration - SCVMM only
  • Shutdown command file duration
  • Built-in duration of 2 minutes (this consists of a 10 second OS shutdown duration and a 60 second OS shutdown duration; rounded up)

The event occurs with either of the following conditions:

Condition 5 for Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Condition 6 for Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

Solution:

Condition 1 for all configurations except VMware and Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 2 for all configurations except VMware and Hyper-V:

  1. Remove some equipment from the UPS to increase the available runtime.
  2. Decrease the shutdown duration time for the UPS On Battery event.
  3. Decrease the command file execution time using the Shutdown Settings screen.

This event is logged and event actions are carried out even if it occurs on a single UPS in a
Redundant or Parallel UPS configuration.

Condition 3 for VMware:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 4 for VMware:

  1. Remove some equipment from the UPS to increase the available runtime.
  2. Decrease the shutdown duration time for the UPS On Battery event.
  3. Decrease the command file execution time using the Shutdown Settings screen.

This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.

Condition 5 for Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 6 for Hyper-V:

  1. Remove some equipment from the UPS to increase the available runtime.
  2. Decrease the shutdown duration time for the UPS On Battery event.
  3. Decrease the command file execution time using the Shutdown Settings screen.

This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:44 PM . Last Modified: ‎2024-03-12 01:10 AM

0 Likes
0
606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:44 PM . Last Modified: ‎2024-03-12 01:10 AM

Hi,

Sorry for the inconvenience. Available runtime has been exceeded is discussed on page 78 of the PowerChute Network Shutdown Hyper-V User's Guide. http://www.apc.com/salestools/PMAR-9E5LP4/PMAR-9E5LP4_R3_EN.pdf?sdirect=true

In Schneider Electric FAQ FA241713 "PowerChute Network Shutdown reports "Available runtime has been exceeded" and by clicking on help in the PowerChute web interface.

I cannot be sure with out seeing he pcnsconfig.ini and the NMC config.ini however in 99% of cases you need to increase the low battery threshold in the NMC to be 2 minutes greater that need needed time for PowerChute to shutdown the OS. The NMC ships with the low battery threshold default of 2 minutes PowerChute needs a minimum of 4 minutes (greater when powering down VMs) so by increasing the low battery threshold in the NMC to 4 minutes the error will be resolved. 

Below is the text from the FAQ

Issue:
PowerChute Network Shutdown reports "Available runtime has been exceeded". and or PowerChute shuts down OS due to "Available runtime has been exceeded"

Product:
PowerChute Network Shutdown versions 3.1, 4.x

Environment:
All supported OS

Cause:
Condition 1 for all configurations except VMware and Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Condition 2 for all configurations except VMware and Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

For  conditions 3 and 4 below, the "total shutdown time" includes the following durations:

  • VM migration duration
  • VM shutdown and startup duration
  • vApp shutdown and startup duration
  • Shutdown command file duration
  • Built-in duration of 2 minutes (this consists of a 10 second OS shutdown duration and a 60 second OS shutdown duration; rounded up)

The event occurs with either of the following conditions:

Condition 3 for VMware:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Condition 4 for VMware:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

For conditions 5 and 6 below, the "total shutdown time" includes the following durations:

  • VM migration duration - Hyper-V only
  • VM shutdown and startup duration- Hyper-V only
  • Host Maintenance duration - SCVMM only
  • Shutdown command file duration
  • Built-in duration of 2 minutes (this consists of a 10 second OS shutdown duration and a 60 second OS shutdown duration; rounded up)

The event occurs with either of the following conditions:

Condition 5 for Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Condition 6 for Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

Solution:

Condition 1 for all configurations except VMware and Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 2 for all configurations except VMware and Hyper-V:

  1. Remove some equipment from the UPS to increase the available runtime.
  2. Decrease the shutdown duration time for the UPS On Battery event.
  3. Decrease the command file execution time using the Shutdown Settings screen.

This event is logged and event actions are carried out even if it occurs on a single UPS in a
Redundant or Parallel UPS configuration.

Condition 3 for VMware:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 4 for VMware:

  1. Remove some equipment from the UPS to increase the available runtime.
  2. Decrease the shutdown duration time for the UPS On Battery event.
  3. Decrease the command file execution time using the Shutdown Settings screen.

This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.

Condition 5 for Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 6 for Hyper-V:

  1. Remove some equipment from the UPS to increase the available runtime.
  2. Decrease the shutdown duration time for the UPS On Battery event.
  3. Decrease the command file execution time using the Shutdown Settings screen.

This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of