We have an HP Proliant Server that is used to host a Hyper-V Virtualised System.
I have just installed updates on 4 Windows Guests and successfully rebooted each in turn to complete the upgrade process. BUT I had a problem with the Host OS (Windows 2008 R2) - following the upgrade I got the following events in the event log followed by a shutdown;
09/29/2017 22:50:56 Available runtime has been exceeded.
09/29/2017 22:50:56 Communication has been established.
There are no events on the UPS Network Management Card 2?
This is the third system I have had this problem with.
Does anyone have a solution to this problem other than to disable the "Available runtime has been exceeded" event?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:44 PM . Last Modified: 2024-03-12 01:10 AM
Hi,
Sorry for the inconvenience. Available runtime has been exceeded is discussed on page 78 of the PowerChute Network Shutdown Hyper-V User's Guide. http://www.apc.com/salestools/PMAR-9E5LP4/PMAR-9E5LP4_R3_EN.pdf?sdirect=true
In Schneider Electric FAQ FA241713 "PowerChute Network Shutdown reports "Available runtime has been exceeded" and by clicking on help in the PowerChute web interface.
I cannot be sure with out seeing he pcnsconfig.ini and the NMC config.ini however in 99% of cases you need to increase the low battery threshold in the NMC to be 2 minutes greater that need needed time for PowerChute to shutdown the OS. The NMC ships with the low battery threshold default of 2 minutes PowerChute needs a minimum of 4 minutes (greater when powering down VMs) so by increasing the low battery threshold in the NMC to 4 minutes the error will be resolved.
Below is the text from the FAQ
Issue:
PowerChute Network Shutdown reports "Available runtime has been exceeded". and or PowerChute shuts down OS due to "Available runtime has been exceeded"
Product:
PowerChute Network Shutdown versions 3.1, 4.x
Environment:
All supported OS
Cause:
Condition 1 for all configurations except VMware and Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.
Condition 2 for all configurations except VMware and Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.
For conditions 3 and 4 below, the "total shutdown time" includes the following durations:
The event occurs with either of the following conditions:
Condition 3 for VMware:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.
Condition 4 for VMware:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.
For conditions 5 and 6 below, the "total shutdown time" includes the following durations:
The event occurs with either of the following conditions:
Condition 5 for Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.
Condition 6 for Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.
Solution:
Condition 1 for all configurations except VMware and Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.
Condition 2 for all configurations except VMware and Hyper-V:
This event is logged and event actions are carried out even if it occurs on a single UPS in a
Redundant or Parallel UPS configuration.
Condition 3 for VMware:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.
Condition 4 for VMware:
This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.
Condition 5 for Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.
Condition 6 for Hyper-V:
This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:44 PM . Last Modified: 2024-03-12 01:10 AM
Hi,
Sorry for the inconvenience. Available runtime has been exceeded is discussed on page 78 of the PowerChute Network Shutdown Hyper-V User's Guide. http://www.apc.com/salestools/PMAR-9E5LP4/PMAR-9E5LP4_R3_EN.pdf?sdirect=true
In Schneider Electric FAQ FA241713 "PowerChute Network Shutdown reports "Available runtime has been exceeded" and by clicking on help in the PowerChute web interface.
I cannot be sure with out seeing he pcnsconfig.ini and the NMC config.ini however in 99% of cases you need to increase the low battery threshold in the NMC to be 2 minutes greater that need needed time for PowerChute to shutdown the OS. The NMC ships with the low battery threshold default of 2 minutes PowerChute needs a minimum of 4 minutes (greater when powering down VMs) so by increasing the low battery threshold in the NMC to 4 minutes the error will be resolved.
Below is the text from the FAQ
Issue:
PowerChute Network Shutdown reports "Available runtime has been exceeded". and or PowerChute shuts down OS due to "Available runtime has been exceeded"
Product:
PowerChute Network Shutdown versions 3.1, 4.x
Environment:
All supported OS
Cause:
Condition 1 for all configurations except VMware and Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.
Condition 2 for all configurations except VMware and Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.
For conditions 3 and 4 below, the "total shutdown time" includes the following durations:
The event occurs with either of the following conditions:
Condition 3 for VMware:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.
Condition 4 for VMware:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.
For conditions 5 and 6 below, the "total shutdown time" includes the following durations:
The event occurs with either of the following conditions:
Condition 5 for Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.
Condition 6 for Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.
Solution:
Condition 1 for all configurations except VMware and Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.
Condition 2 for all configurations except VMware and Hyper-V:
This event is logged and event actions are carried out even if it occurs on a single UPS in a
Redundant or Parallel UPS configuration.
Condition 3 for VMware:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.
Condition 4 for VMware:
This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.
Condition 5 for Hyper-V:
Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.
Condition 6 for Hyper-V:
This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.