PowerChute Client 3.0.1a shuts servers down - no power event from UPS logged

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Client 3.0.1a shuts servers down - no power event from UPS logged
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

0 Likes
3
646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

PowerChute Client 3.0.1a shuts servers down - no power event from UPS logged

Hi

I have a smart-ups RT3000 on a client site.  All servers have PowerChute Network Shutdown client version 3.0.1a (says latest version installed)  on Friday at 11.45pm the PowerChute client sent a shutdown command to all servers.  The UPS did not email any power events and nothing is logged.  Checking the PCNS event log I see the following:

05/28/2013 14:52 UPS has switched to battery power

05/28/2013 14:52 Input power has been restored:  UPS has switched to On Line operation

05/31/2013 23:44 Available runtime has exceeded

05/31/2013 23:44 Shutdown process started.  Windows  will shutdown soon.

APC model:  AP9631

Hardware revision: 05

Application Module

Name:     sumx

Version:     v5.1.3

APC OS

Name:     aos

Version:     v5.1.3

APC Boot Monitor

Name:     bootman

Version:     v1.0.1

Any help someone can give would be greatful.

Thanks


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

0 Likes
0
646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

PCNS started the shutdown because of the low runtime issue at 23:44

05/31/2013 23:44 Available runtime has exceeded

05/31/2013 23:44 Shutdown process started.  Windows  will shutdown soon.

Low runtime can be caused by low battery or by misconfiguration. Below is from the help file

Available runtime has been exceeded The UPS does not have the runtime available that is configured in PowerChute Network Shutdown. Two configuration conditions can cause this event:
  • When the command file time on the Configure Shutdown page plus 10 seconds is greater than the Low Battery Duration field value. (A low battery condition always causes a shutdown, so when it occurs the UPS must have enough time available to complete shutdown activities). To fix this, either decrease the command file time, or increase the Low Battery Duration value. (To change the Low Battery Duration, on the Network Management Card user interface select the UPS tab and Configuration - shutdown).
  • When the UPS runtime is less than the sum of the shutdown delay time configured for the UPS: On Battery event plus the command file time on the Configure Shutdown page, minus two minutes. This condition can be caused by having too much load on the UPS, or by the UPS batteries not being fully charged. If the UPS batteries are fully charged, to fix this a) remove some equipment from the UPS, or b) decrease the shutdown delay time for the UPS: On Battery event, or c) decrease the command file execution time on the Configure Shutdown page.

This event is always logged and, on a Redundant-UPS configuration, event actions are carried out even if it occurs on only one Network Management Card.


Hope this info helps.


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

0 Likes
0
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

Hi,

You should check the PCNS configuration. The log indicates the shutdown was started due to Available Runtime being exceeded. If you don't want the systems shutdown for this event you can deselect it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

0 Likes
0
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

Hi Bill P.

Thanks for your response.  I have no issues with the servers being shutdown if there are power issues.  My problem being is that there were no power issues on Friday, the UPS did not run from battery at all so why would the client think that the available runtime is exceeded as it had full power. There is nothing logged on the UPS to say it even switched over to battery at all on the 31st.

This is my concern, why did PCNS shutdown my servers when there were no issues?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

0 Likes
0
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-13 12:12 AM

PCNS started the shutdown because of the low runtime issue at 23:44

05/31/2013 23:44 Available runtime has exceeded

05/31/2013 23:44 Shutdown process started.  Windows  will shutdown soon.

Low runtime can be caused by low battery or by misconfiguration. Below is from the help file

Available runtime has been exceeded The UPS does not have the runtime available that is configured in PowerChute Network Shutdown. Two configuration conditions can cause this event:
  • When the command file time on the Configure Shutdown page plus 10 seconds is greater than the Low Battery Duration field value. (A low battery condition always causes a shutdown, so when it occurs the UPS must have enough time available to complete shutdown activities). To fix this, either decrease the command file time, or increase the Low Battery Duration value. (To change the Low Battery Duration, on the Network Management Card user interface select the UPS tab and Configuration - shutdown).
  • When the UPS runtime is less than the sum of the shutdown delay time configured for the UPS: On Battery event plus the command file time on the Configure Shutdown page, minus two minutes. This condition can be caused by having too much load on the UPS, or by the UPS batteries not being fully charged. If the UPS batteries are fully charged, to fix this a) remove some equipment from the UPS, or b) decrease the shutdown delay time for the UPS: On Battery event, or c) decrease the command file execution time on the Configure Shutdown page.

This event is always logged and, on a Redundant-UPS configuration, event actions are carried out even if it occurs on only one Network Management Card.


Hope this info helps.


Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of