PowerChute Business Edition and Hyper-V Core 2016

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Business Edition and Hyper-V Core 2016
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
3
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

PowerChute Business Edition and Hyper-V Core 2016

I installed PowerChute (10.x) on the server core. It found the UPS and the Agent service runs fine. Now I try to (remotely) connect to the agent using a web browser https://:6547, but to no avail. Doesn't make a difference if I use the FQDN or IP-address. Restarted the Agent service a couple of times, but nope. Performed netstat -a and notice the localhost (0.0.0.0) is listening on port 6547, but it's not listening on the core's IP-address. Removed and re-installed the software, but that doesn't make a difference. How to get things going?

Simon

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • hyper-v
  • powerchute-business-edition
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
2354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

Right, I had to (manually) open port 6547 on the core firewall. When installing the Agent, it asks to add a firewall exception, but it doesn't. Executed this command on the Core Console: netsh advfirewall firewall add rule name="APC Agent 6547" dir=in action=allow protocol=tcp localport=6547 and after that, I can connect to the agent with the web browser.

Simon

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
2354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

Hello,

When running netstat - a the port should be listed as TCP  Local Address 0.0.0.0:6547 Foreign Address Domain Name:0  State = Listening You should also see TCP Local Address [::]:6547 Foreign Address Domain Name:0 State = Listening

You can check the status of the firewall using Powershell The command is Get-NetFirewallProfile 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:23 PM . Last Modified: ‎2024-02-14 11:57 PM

Right, I had to (manually) open port 6547 on the core firewall. When installing the Agent, it asks to add a firewall exception, but it doesn't. Executed this command on the Core Console: netsh advfirewall firewall add rule name="APC Agent 6547" dir=in action=allow protocol=tcp localport=6547 and after that, I can connect to the agent with the web browser.

Simon

Reply

Link copied. Please paste this link to share this article on your social media post.

josh3
josh3
Cadet

Posted: ‎2021-11-05 02:26 PM

0 Likes
0
2265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-05 02:26 PM

I am having the same problem, but this is with Hyper-V Core 2019.  Started, Stopped and restarted the agent; reinstalled the agent; added the manual firewall rule and port 6547 is still not listening.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore